I've been asked to fit a new consumer unit in an old property. One issue that I have found straight away is that the lighting would seem to have no cpc (old 2 wire cables). Ideally I would advise to have the lighting circuit rewired but the 1st floor of the property has a flat roof with no apparent easy access to the cables. Is there an acceptable way around this? Perhaps ensuring all light fittings and switches are class II and putting a limitation/departure on the certificate?

Thanks
 
You cannot use Class II as a measure of protection if this is a dwelling nor can you obtain Class II switches. You cannot enter a Limitation on an EIC and a departure must ensure that the measures of protection are not any less than required by BS7671.
 
Thanks for the reply Westward10.

In that case is a rewire essential? I have seen class II light fittings advertised as not requiring earth and considered wireless switches. More expense than the client was expecting but a rewire of the 1st floor lighting would be even more drastic I suspect.... :(
 
Have a read of this best practice guide. Page 10 deals with your situation.
You will see that as an absolute last resort it's possible to reconnect lighting circuits with no CPC if certain criteria are met.

https://www.google.com/url?sa=t&source=web&cd=&ved=2ahUKEwjPgsni56PtAhXDh1wKHRKkC30QFjAAegQIAxAC&url=https://www.electricalsafetyfirst.org.uk/media/1203/best-practice-guide-1-issue-3.pdf&usg=AOvVaw066MiiA9r2sYdfidSUbI1B
Thanks again. 10.4 seems to be the best suggestions...
 

Reply to New consumer unit but lighting has no earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
232
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
532
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
NICEIC Certification Scheme SPD on old consumer unit?
Under amendment 2 of the BS7671, there is now a requirement to fit an SPD as standard. I am due to install a new outdoor socket circuit on an...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock