We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
 
If you’re talking about ring circuits ? then you need to get your capitals correct
r1 rn and r2 are for ring final circuits and are different from R1 and R2 which is the resistance or impedance of the line and cpc
 
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
 
We all know how to and why we get the 1/4 value, but to what, if anything do we add to that figure and into what box on the cert does it go, depends on who you ask/assessor is apparently,
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
 
If you add the (R1+R2) to the Zdb then this will give you an indication as to the expected maximum Zs for the ring final circuit.
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
OK lets take some actual numbers, Ze or Zdb .22, on the ring Live .45. CPC .76 So 1.21 / 4 = .30 That figure is only used to check around the RFC for higher than expected readings It goes nowhere on the cert, what does go on the cert is the sum of ZE & R1+R2 which is 1.43 which is Max measured ZS only its not, its the
sum of the readings, to get a measured ZS its a live test done at a socket as that is the only real result . However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer
 
However according to other informed sources the Box asking for max measured ZS should be the 1/4 value plus Zdb which is .52 in the above example not the 1.43 using ZS = ZE +R1+R2 that said I will stick to the way I was trained ZS is Ze +R1 +R2 there is no other answer

No, the max measured is the maximum value which has been measured.
A measured value is not calculated, it is measured.
 
  • Like
Reactions: loz2754 and DPG
If you have measured all tests correctly on a ring final circuit & checked the r1 + r2 /4, you will have all the necessary check sums & measured results ( Ze, Zs Zdb) to fill out the cert. So whats the problem ! Maybe( R ) Stands for Radial !
 
No, the max measured is the maximum value which has been measured.
A measured value is not calculated, it is measured.
I understand but can you explain this, its from an example eicr in a well know textbook R1 .46 R2 .76 r1+r2 = 0.08 ? with a max measured Zs of .37
 
The r1+ r2/4 figure is really only used as a comparison or check to see if the actual R1+R2 readings at each point on the ring are as you expect them to be.
The only figure you record on the schedule of test results is the highest measured R1+R2 value.
It doesn't depend on who you ask. It's plainly written down in GN3 and other readily available publications.
It's plainly written down in GN3 and other readily available publications. can you tell me the page
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

the pict

Mentor
~
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
R1 R2 Chestnut time again
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Tags Tags
again time

Advert

Thread statistics

Created
the pict,
Last reply from
nicebutdim,
Replies
9
Views
1,723

Advert