david42
Problem as above - is a disconnected earth wire in a socket sufficient to cause this? If so, I would like a brief explanation of the safety mechanism involved.
a real fault.In one word - NO.
Is this a real fault or a college task?
Hi - is a disconnected earth wire a short circuit ?That fault sounds strange as a short circuit to operate the MCB would not cause the RCD to trip unless it were faulty, if it were a fault to earth the RCD would trip without the MCB.
For both to happen would indicate a double fault perhaps a neutral earth fault of high resistance in another circuit protected by the RCD that only causes it to trip when there is a very high current e.g. a short circuit on the ring.
Think the OP may be he seems a bit long in the tooth to be at college, hope you don't mind me mentioning that factIn one word - NO.
Is this a real fault or a college task?
Getting touchy in your old age Tel? you are correct of course, but I thought I was the only person getting all vexed when people call a RFC a ring main.hust on a matter of terminology, david, it's a ring final. a ring main only applies to a supply circuit wired as a ring.
i also refuse to call a henry or a dyson a hoover.Think the OP may be he seems a bit long in the tooth to be at college, hope you don't mind me mentioning that fact
Getting touchy in your old age Tel? you are correct of course, but I thought I was the only person getting all vexed when people call a RFC a ring main.![]()
Ours is called Oleg, don't ask why please, I don't know.i also refuse to call a henry or a dyson a hoover.
What type of test kit ?Back to the op.... If the RCD and mcb are tripping you need test kit....
What type of test kit ?
What type of test kit ?