I've never noticed that before! socket RCDs are BS7288 and max trip time on 1x is 200ms. thats my lesson learnt for the day.
 
  • Like
Reactions: 1 person
300mSec. at x1. unless it's a TT system, where it's 200mSec if the RCD is used for fault protection.
 
  • Like
Reactions: 1 person
I believe it changed from 200 to 300 when it went from 16th to 17th edition, for 61008 and 61009 at least.
 
I believe it changed from 200 to 300 when it went from 16th to 17th edition, for 61008 and 61009 at least.

Could be right there.
I always thought it was 40ms @ 5x because that's a fifth of 200. 300 is just confusing!
 
It depends on the BS number. GN3, BGB and OSG has all the info needed

Cheers...........Howard
 
Could be right there.
I always thought it was 40ms @ 5x because that's a fifth of 200. 300 is just confusing!

If we stick to the 200ms, least we'll be edging on the safe side. Though I can't recall seeing one above 54ms in my limited time of being let loose with an MFT (and that turned out to be my winky connections!).
 
  • Like
Reactions: 1 person
The 40ms at 5x stayed the same, don't understand why they changed the 1x to 300 really anyway as its not 5x40 which made made sense before.....the 5x test is the only one it has to pass anyway I seem to recall, although I would be changing the Rcd if it failed 1x anyway
i also have had over 100ms trip times before on one side of the cycle usually.
 
  • Like
Reactions: 1 person
Aye, fifth of an Amp, you're into dangerous territory, <<40ms the better!

With any luck, Professor Cockburn will be along soon to enlighten us all further.
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
tripping times?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
debutant,
Last reply from
Silly Sausage,
Replies
20
Views
3,515

Advert