Had a weird one today. Doing an EICR and the lady says yeah we dont touch the screws at the switches or sockets as we get a shock from them. I said yeah?? Went to unscrew a light switch and sure enough zap.
Touched it again and nothing so i was thinking static.
Tested the house ze 0.14 tncs system lighting circuit r1r2 0.34 zs 0.56 rcbo x1 21.8 everything fantastic went to screw back the switch zap again. Then nothing. No voltage between earth connection and neutral but 8-10 ohm between live and earth. Is it just static?
Touched it again and nothing so i was thinking static.
Tested the house ze 0.14 tncs system lighting circuit r1r2 0.34 zs 0.56 rcbo x1 21.8 everything fantastic went to screw back the switch zap again. Then nothing. No voltage between earth connection and neutral but 8-10 ohm between live and earth. Is it just static?