Had a weird one today. Doing an EICR and the lady says yeah we dont touch the screws at the switches or sockets as we get a shock from them. I said yeah?? Went to unscrew a light switch and sure enough zap.

Touched it again and nothing so i was thinking static.

Tested the house ze 0.14 tncs system lighting circuit r1r2 0.34 zs 0.56 rcbo x1 21.8 everything fantastic went to screw back the switch zap again. Then nothing. No voltage between earth connection and neutral but 8-10 ohm between live and earth. Is it just static?
 
If you have 10 Ohms between live and earth, then it isn't a static electricity problem . And if it was static, it wouldn't occur every time you touched the switch plate - it would have to build up again.
 
Sounds like static to me, if you get a shock from a well earthed thing, then immediately after all is fine when you touch it.

A resistance between live and earth when all is dead is normal, earth and neutral are connected together at source, live to neutral are connected by the loads on circuits.
 
It is not happening all the time. It will happen then i can touch it and there is nothing. Strange thing is though i can touch the earth connection with the probes of my meeger and you can see and hear the zap, i can instantly touch it afterwards though. The probes are obviously metal but they are rubber insulated so if it was static how could that pass through me onto insulated holders to the metal tips? Very confused.
 
I not convinced this is static. The occasional static zap maybe, but this sounds far too often.

Unless they have nylon carpets, or a Vaan de Graaf generator in the kitchen.
 
If you have a good earth
And a good connection from device to earth, then the potential at that point is 0V
You can’t get a shock from something that is well earthed unless you have potential yourself.
But I agree with your point @DPG it sounds far more often than I would expect.
 
Had this in an office with nylon carpet tiles and when the panel heaters were on the air would dry out.

Staff would often get static shocks so as an experiment I placed a bowl of water out of harms way and within a couple of hours the static shocks had reduced.

They now have a small humidifier and this works a treat.
 
With rcbo off but main switch on 8 - 10 ohm between l and e on continuity tester. Ir test is greater than 299 on every circuit
[automerge]1570137908[/automerge]
With main switch off, the 8-10 ohm disappears but the tester just clicks on off on off on off for continuity
 
With rcbo off but main switch on 8 - 10 ohm between l and e on continuity tester. Ir test is greater than 299 on every circuit
[automerge]1570137908[/automerge]
With main switch off, the 8-10 ohm disappears but the tester just clicks on off on off on off for continuity
Sounds like your picking up the circuitry within the RCBO. What continuity do you get with the RCBO disconnected?
 
What disappears. Randomly changing components is only guesswork you need to find the actual problem causing the issue.
 
I never randomly changed anything. As i said the 8 ohm disappears when the live and neutral disconnected from rcbo so i suspected a faulty rcbo. I changed it to see if a new one had tbe same result. It did.
 
... Strange thing is though i can touch the earth connection with the probes of my meeger and you can see and hear the zap,
If you can get 6mm of spark , that's aprox 10kV of static .

(was it pretty toasty there ? (mid winter also works when ground frozen))
Moving around -from shoes , sliding over a carpet / getting up from seating - will also re-charge you.
(If they are having computer problems - Ionisers /van der graaf !)
 
Just to confirm, do you mean 10 Ohm live to earth, or 10MOhm when you test IR?
 

Reply to Weird Earth Fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
It's not power that decides how far a spark will jump or how insulation will break down, it's voltage, With the peak voltage of 230V mains being...
Replies
17
Views
3K
Yeah it is quite dramatic hehe but when the lighting is on a ceiling rose which they use in UK, it has a lot of terminals for the normal halogen...
    • Like
2
Replies
25
Views
7K
It is highly unlikely you are getting the sensation of electricity. The pan is isolated from the induction coil by the glass top, any voltage...
Replies
4
Views
1K
  • Question
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...
Replies
13
Views
3K
  • Question
So, an update - UK power networks came out that night at 9pm (very impressed with that) - checked everything at the customer's cutout, the...
2
Replies
25
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks