Hello,

I have a question about replacing the programmer in my central heating controls.
I currently have a very basic Honeywell timer/programmer connected to the heating system via the Y-plan.

I would like to replace it with a USB controlled relay. So that I can control the heating and hot water via a computer.
(I would link to a page about the relay, but because I'm new here the board won't let me. But you can google for UDIN-44 if you want more info.)

photo5jm.jpg

screenshot20120929at112.png
I am not an electrician, and I will be employing an electrician to do the work, but I would like to understand the required wiring before I employ them, so that I can explain what I would like. Please could I ask your advice? (I'm not familiar with A/C electrics, but do have some experience with 5v electronics theory.)

So - as far as I can work it out in the y-plan at the programmer you have Neutral, Live and connections 1,2,3,4 (DHW Off, HTG Off, DHW On, HTG On). Obviously the On and Off Pins for each system are mutually exclusive - e.g. either DHW On (pin 3) is connected to Live or DHW Off (pin 1) is connected to live - but never both (and the same for the HTG pins.)

What I don't understand is how the neutral connection is connected - from the internal wiring diagram of my programmer and the y-plan schematic it appears that N and L are basically connected together inside the programmer - wouldn't this be a short circuit? Or is that just to provide power for the programmer itself?

Basically what I'm asking is - in my four relays can I just connect live to the central poles and pins 1-4 to the four contacts, or does neutral need to be connected too?

Thanks for any advice.
 
What I don't understand is how the neutral connection is connected - from the internal wiring diagram of my programmer and the y-plan schematic it appears that N and L are basically connected together inside the programmer - wouldn't this be a short circuit? Or is that just to provide power for the programmer itself?

Basically what I'm asking is - in my four relays can I just connect live to the central poles and pins 1-4 to the four contacts, or does neutral need to be connected too?

Welcome to the forum.

The diagram shows L and N connected to "Clock" so, yes, the neutral is just required to power the programmer's internal timer.

And, yes, connecting the two common central poles (2 and 5 from the left in the bottom row) to live and the four relay outputs to the CH on, CH off, HW on and HW off would work. If it's a Y plan you'll probably find that one of the "offs" is not required and not currently used (can't remember which).

You would perhaps have been better to have used two single pole, double throw relays rather than four single pole, single throw relays; you'll have to make sure that you don't energise an "on" and a corresponding "off" at the same time.
 
wish i could help
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Y-Plan wiring theory advice (replacing programmer)
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
Diggory,
Last reply from
SYKRAPS,
Replies
5
Views
4,389

Advert