Inspection of property.
lighting grid switch outside downstairs loo, 3 switches.
One intermediate for stairs lighting, one one pole 2 way for downstairs corridor lighting.
Its the 3rd switch that bothers me. Its a double pole switch, and they have used one pole for the switched live for the loo, and the other pole for the switched live for the fan, the power for the fan is off the 2nd floor ring main via a 3A fuse switch spur, and the local fan isolator switch is after the double pole switch.
This means that if a less suspecting person, or even a DIY home owner turned off even all the lighting circuits there would still be a live wire present for the fan off the ring main.
This just seems wrong to me, but can't think of a reg that applies to it, can you?
lighting grid switch outside downstairs loo, 3 switches.
One intermediate for stairs lighting, one one pole 2 way for downstairs corridor lighting.
Its the 3rd switch that bothers me. Its a double pole switch, and they have used one pole for the switched live for the loo, and the other pole for the switched live for the fan, the power for the fan is off the 2nd floor ring main via a 3A fuse switch spur, and the local fan isolator switch is after the double pole switch.