Hi guys. I have recently come across a N-E fault on the garage supply. the cable that was used is a 2-core SWA 6mm. However due to the house it is not possible to run a new cable to the garage. However there is a sub-board upstairs which is fed off a 40A MCB from the main lighting board, non rcd-protected. The sub board has a 100A main switch with a 63A rcd which protects 3 circuits. x2 rings and a lighting circuit. I was thinking of running the new garage supply from this board? Is this allowed? The run is about 15M and will be clipped direct. The garage runs a hot tub protected by a B32A MCB, a 16A radial and a 6A lighting circuit. I was thinking of running 6mm 3-core SWA to supply the garage. Which will be protected by a type b 32A mcb from the upstairs sub board. Just need confirmation please. Thanks.
Well you have no discrimination between the two 32As but you wouldn't have it anyway with mcbs protecting mcbs.
You can run your new supply to the garage from wherever it takes your fancy
Before you decide from what location, you need to assess the existing cable size,the protection it affords, the present load and whether it has the capacity to cope with the calculated additional load and the earthing requirements and protection of that load
These questions are often encountered by electricians who have trained to obtain the skill to adequately answer so that the installation is safe for the user
There are people who just add cables to connections points and get things working, safety is not considered and/or mostly understood,but there are people who seek help or advise from those with the training to assess these installations
Shoving loads on systems willy nilli is not recommended
over load if done !
Well currently the cable that supplys the garage is a 2-core and they have used the sheath as the earth. It then goes into a 2-way garage unit. The hot tub people have linked a bit of 6mm from the main switch into there rcd unit to supply the hot tub. Will probaly install a 4-way board when i run the new supply cable to the garage.
My description is confusion i apologies. The sub main is supplied from a 40A McB using 10mm T+E. It has a ring circuit and a lighting circuit. So if i were to calculate total load of them circuits + the total load of the circuits for the garage, aslong as thats under 40A it should be fine? My question is can you run a sub main off another submain?
Outside power to a hot tub, where already an SWA cable has failed ... hmmm, isn't this something you'd like to have an expert look at? What type of earthing system do you have, how will you handle bonding? Not to mention this work requires building approval, for very sound safety reasons in this case.
The swa for the hot tub supply hasent failed. Its the swa that supplys the garage fuse board tripped out the main rccb due to a neutral-earth fault. Its an old cable and it probaly has deterioated over years thats why there is a fault on it. So now i need to replace the cable, however the route it takes is covered by expensive hard flooring and routes under the house and paving slabs. Therefore an easier route to take would be off the sub-board upstairs, however that is supplied from a 40A MCB. The system is TN-S.
we on this forum can not do the job for you ,we can( only advise .)
having you read all the posts it is down to you how you do the job.
but if I was you, which I'm not I would put a new feed to the garage
and tell your customer .
Thats fair enough. Ive only been qualified for a year, so im still gaining experience and learning new things every day. Thats why i posted this just for advice, I just wanted to know if what i proposed to do was safe and complys with regs.
Fair enough your still learning your trade, and well done for asking when your not 100% sure. A good trait........
When you boil it down you have a 40A MCB supplying 2 x ring mains, a 32A hot tub, a 16A radial (which you haven't given any details of) and 2 lighting circuits. You must see that this is likely to overload the 40?
As much as a pain as it is, you need to tell your customer that they need to replace the supply to the garage.
Its not easy when you are just starting to tell the client "bad news" and other chancers may come along and do just what you said. However if you intend to be a decent Electrician you must get used to the idea that the customer is not always right.
wow, how did you come to that, read post 6!
Thanks for the reply. And i an see exactly where your coming from. I havent looked into this in detail so i dont even know what size cable they have used to supply the submain. So if its the max cable size for that 40A MCB then i will not supply the garage and will have to find another route. The old garage supply runs under the house which has a 450mm deep void, fingers crossed I can fish the new supply that way!
Spot on, almost anyone can make it "work" but make no attempt, or incapable of dealing with possible faults that may lie ahead, "risk assessment" does not come into it. I have, like many on here, seen incredible botch ups. In the long run its just as easy to do it the right way, yes and spend a bit extra, to ensure everyone's safe operation of the things you install. I had an admiral very proud of his work in his own home, yes all the sockets worked, wired in 1mm t/e connected to existing ring circuit, yeah it worked. Supply to his stables, oh boy, again 1mm t/e spade slot across the lawn then up the drain pipe and under the eves to a consumers unit, yeah it worked! I know and trained people on here know how to assess these situations and know what has to be done for a proper installation. I so dislike DIY know it alls.
Reply to Running new cable to supply garage from sub-board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...