You will need RCD protection somewhere is virtually every case. If it is fed via SWA cable so no need for protection on the distribution cable then it makes sense to have just a MCB at the house CU and then RCD and any other MCBs at the garage.

However, if you can't be sure of the sub-main installation then having RCD/RCBO at house and then just MCB at the garage is a better choice.

Two 30mA RCD in series without selectivity is poor design, not enough to worry about on an EICR beyond C3, but not something you should aim to do unless you have a very good reason.

Having said that, having MCB in series or RCBO+MCB will have negligible fault selectivity, even if they are OK on overload due to a 1.6:1 or greater difference in rated current. Again, not good design, but usually an acceptable trade-off if the final circuits in the garage are not critical as done in practically every case.
I knew there was an issue with RCDs in same circuit. I did not know MCBs would be an issue and quite surprised. I agree no other way of doing it. I am sourcing a garage unit with 2 MCBs and a 2 pole isolator. This will be run of the main CU which is a dual board with 32A MCB and RCCB type A, thankfully. Thanks for your help. You are very knowledgeable. I see alot of ppl using those plug RCDs when using power tools on circuits with RCBOs or RCCBs. Wonder what potential effect that would have?
 
I see alot of ppl using those plug RCDs when using power tools on circuits with RCBOs or RCCBs. Wonder what potential effect that would have?
It is perfectly safe - at least one of the RCD will trip - it is just inconvenient to have to reset two devices, and a possible hazard if the upstream device also feeds something like stair lights that you don't want failing.
 
  • Like
Reactions: DPG and Jonny72
Ya that's the main disadvantage of the upstream RCD

Loss of lighting on a socket fault in shed
 
  • Agree
Reactions: pc1966
Ya that's the main disadvantage of the upstream RCD

Loss of lighting on a socket fault in shed
If its a workshop shed then probably best option is emergency lights, that way any cause of power failure results in some lighting, not darkness and power tools still running!
 
  • Like
Reactions: Mikegh
just buy the cheapest garage board , buy a seperate 80a switch and swap it out. in the grand scheme of a job it adds about a tenner to the material cost
Yep, that’s what I do. That spare RCD has always come in handy down the line.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Garage Consumer Units
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Jonny72,
Last reply from
leesrubberroom,
Replies
24
Views
2,341

Advert