Just been to a new house (5 years old) which had no main equipotential bonding to the incoming water. Gas was bonded with 10.0mm
Checked on original EIC and water service box was marked N/A
All pipe work inside the house is copper but the supply pipe is plastic up to main stop tap

Surely this isn't right?
 
Correct, it is not right, the internal metal pipework should be bonded.
There's an unless figure but I can't remember what it is
 
I though it needs bonding unless ALL internal pipe work is plastic.
Might see if neighbors houses are the same.
I assumed there would be no issues with this property with it being so new.
Dual rcd board - check
gas bond - check
water bond - err... It must be here somewhere!
 
Only need to bond a parallel path. Could be a section in plastic, best bet is to test it. If its over 23 000 doesn't require bonding.
 
From OSG "There is no requirement to main bond and incoming service where the incoming service pipe and the pipework in the installation are both of plastic. where there is a plastic incoming service and a metal installation within a premises main bonding is recommended unless it is confirmed that any metal pipework within the building is not introducing an earth potential."

IF an IR test between MEt and the metal pipework give a value <22Kohm then the metal internal pipework should be bonded, if it is greater than that then there is no need to bond as it is not introducing an earth potential.

There is some variation in the IR figure depending on who you listen to but generally if it is not connected to earth then there is not need to bond plastic incomers.
 
So am i right in thinking that if the main feed, stop tap and (for arguments sake) 1st 6m of consumers pipe is plastic, but the rest is copper you bond your main bonding as soon as it changes to copper?

I have never actually worked on a property like that before so its new to me.
 
I would carry out a continuity test. And if over 23k ohms then it does not need bonding. Taking this from a 'safe' touch current of 10mA.
230\0.01= 23,000 ohms

My opinion of the OSG is proving to be more true each time I hear stuff from it. I don't like it to say the least.

Yes if it's all plastic and you can see it is. Then it's pointless testing.
But if there's any copper id check as its your --- on the line if it ain't right.
 
Well it's all copper so needs testing.
Entire plumbing install is copper right up to the supply pipe.
 
From OSG "There is no requirement to main bond and incoming service where the incoming service pipe and the pipework in the installation are both of plastic. where there is a plastic incoming service and a metal installation within a premises main bonding is recommended unless it is confirmed that any metal pipework within the building is not introducing an earth potential."

IF an IR test between MEt and the metal pipework give a value <22Kohm then the metal internal pipework should be bonded, if it is greater than that then there is no need to bond as it is not introducing an earth potential.

There is some variation in the IR figure depending on who you listen to but generally if it is not connected to earth then there is not need to bond plastic incomers.

Surely an IR test is not the best idea. Introducing unnecessary voltage onto pipe work. Especially if the house is occupied and they are home.

Also the figure depends on the current that is deemed to be safe to touch. 30mA is the max. But most people like to work off 10mA to be on the safe side.
Plus 1000ohms for the resistance of the body.
 
if the property has combi boiler its highly likely unless insulated joints to need bonding as the gas, combi supply earth and water will all be connected together.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New house, no main water bonding
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
ash_s3,
Last reply from
jumpin jax,
Replies
36
Views
18,965

Advert