3.99kWp of panels falls within the 'up to 4.0kWp' FIT tariff - the DNO is not interested in this figure. What the DNO is interested in is the net output from the inverter, which should not exceed 16A for a 'install and inform' type of installation. That 16A figure may equate to a maximum inverter output of 3.68kW or 3.84kW depending on the DNO in question - many DNO work to the 'nominal' network voltage of 230v, permitting a maximum inverter output of 3.68kW, a few DNO work to the 'actual' network design voltage of 240v, so they will permit a maximum of 3.84kW output from the inverter.
The SB 4000TL can be configured to limit its output to either of the maximum amounts above, via use of a 'GridGuard' code, which can be requested from SMA.
Stepping beyond this simplest approach, you can also submit a 'G83 stage 2' request to the DNO, for permission to connect a system exceeding 16A, but operated under G83 rules. If the local network infrastructure is capable of supporting this without remedial work, the DNO may permit you to just go ahead and connect, sometimes they require that minor adjustments are made to the inverter configuration.
Don't think I missed anything.