You will share an earth if its a 3 phase supply coming into a build then spurring off to supply sub section remember this happens in a row of say 4 terraced houses where the DNO takes a 3 phase supply to one house then spur off to the rest now this is not a lecture here but coming on shooting from the hip aint no good for anyone as you can end up running about chasing your tale and yes I have said this before when you post a question give as much info as you can Ze,PFC,PSSC Zs even a global IR test

Just to add a lot of domestic sparks do not realise that supply cables are all 3 phase hence when you lose a phase say in a street then its every third house that has no power an example would be a block of flats where you get a 3 phase neutral and earth entering the building and then it is broken down to single phase supplies to each flat and the neutral and earth are all shared back in the service cupboard
 
Why not go through the board switching off circuits until the voltage clears, then fault find the offending circuit?
 
Why not go through the board switching off circuits until the voltage clears, then fault find the offending circuit?

There are multiple items of switchgear for the neighbouring premises downstairs with one of the downstairs boards being placed upstairs. Other than switching off at the main isolator checks conducted on my visit did not clear the voltage. Agreed but fault finding requires access to the premises.
 
You will share an earth if ...

The earthing block used is pretty similar to this:

http://www.tlc-direct.co.uk/Images/Products/size_3/TLEB8.JPG

This one block is used for the earthing of two premises. It is carrying AC current which, as I explained to the client, has the potential to loosen connection over time through the possible manifestation of vibrations at 50 hertz.

Best case scenario is for the supplier to provide separate supplies for both premises but failing that a new/less worn MET would otherwise be installed.
 
Just go and fix it man ffs.
Are you a house basher, domestic installer or Electrical Trainee?
There is a lot of info being given/suggested here that an apprentice trained spark would know..........or work out!

Boydy
 
My view is that the potential for current flow was checked but not measured. Loop impedance tests checked continuity to earth while the voltage test checked the potential for the flow of a level of current which would clearly provide a potential for harm should further faults develop.

I think the main point I'd like to leave with you is that, even if you measure 95V on a disconnected earth cable, without knowing the impedance of the 'fault' you've no way of knowing what current will flow when the cable is re-connected; it may be trivial. Even a cheap clamp ammeter will give you some idea of what's actually happening in those cables. And it's especially useful for fault finding in situations where you can't disconnect cables for whatever reason.

Edit:
If you want a recommendation for one that will do everything you need, and more, I use a Metrel MD 9270 and find that it reliably gives a stable reading every time:
http://www.test-meter.co.uk/product...l-md-9270-leakage-clamp-with-power-functions/
 