Currently reading:
A good guide For 'exported PME' and outbuildings!

Discuss A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Reaction score
1,512
For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.

It was published in 2005 but the important bits remain unchanged and might be of some help!
 

Attachments

  • Garage-Shed Supplies.pdf
    243.4 KB · Views: 5,858
Good article, but what are the myths?

The biggest myth is 'whoa, you can't export PME'.

Then there's 'if there are extraneous-conductive parts in the outbuilding, you can't export PME.

Then there's 'you must inform the DNO'

There may be more but the exported PME threads normally crop up here on at least a weekly basis and I think I can hear the groans of many members as the myths are propagated again and again!

These contentious issues should be periodically addressed/updated by the IET.

The last guidance on high protective conductor current was published in 2005 and even Guidance Note 8 has still not been revised to reflect 17th edition changes!

Not good enough.
 
Last edited:
Must admit I fell for the contact DNO one a minute ago.
I've never understood where this 'can't export PME' stuff has come from, it's all pretty straightforward if you know your stuff.
If exporting the earth bond back to the MET, if not TT and use your MET in the DB board.
I know there can be more to it, but that's the basis.
 
cant c it on my phone sorry!! as far as i am aware u can take a supply from a existing house CU via a MCB then to another sub CU ran in SWA. if the supply to the house is PME why would u need to put a earth rod in? can u not run a 3core cable and take the earth from the MET in the house??? i think i have miss understood
 
A lot of these myths stem from the numerous ''Scaremongers'' of the PME system!! In that ''IF'' (and it's a very big IF) a break in the neutral occurs all connected metal parts will have a potentially dangerous voltage. In reality, the chances of that happening is remote to say the least. I would take a PME system earth out, to any out-building, wouldn't give it a second thought either

Again In reality, what would you rather have as your earth connection, a system that gives you 0.35ohms or a rod at maybe 200ohms, ...i know what i would rather have in my home.

There is no reason why you can't employ a rod on a PME system, in fact many countries insist on it. Many local authorities used to rod TNS supplies to there council houses in the 50s.
 
Then there's 'if there are extraneous-conductive parts in the outbuilding, you can't export PME.

Then there's 'you must inform the DNO'
Then there's 'you must inform the DNO'



Seems you still haven't quite grasped the point have you. Yes you CAN take PME to an outbuilding with extraneous-conductive parts!! Your not exporting your extending the equipotential zone!! Please read ALL of this thread, or you will be taking the thread back to the very start again with your post above!!

There is NO must inform the DNO, ...about the majority of installations undertaken by electricians, and certainly not in the case of shed in the back garden. Get your facts sorted out please!!!
 
Let's get the terminology right, shall we chaps.

You cannot 'export PME' to outbuildings.:)

Combining the Neutral and Earth on the consumer side of the installation is not allowed in this country.

You can, however, run an Earth, or Bonding Conductor, from your installation MET to an outbuilding - regardless of the supplied earthing system.
You must though, as Designer and Installer, take into account 'Extraneous Conductive Parts' in the outbuilding.
If it's a PME supplied Earthing System, then you would need to bond these back to the MET, as you would any other Extraneous Conductive Part.
This could mean running a 10mm Bonding to the shed to accompany a 2.5 mm socket/lighting feed.:)


The other thing that needs to be taken into consideration is
uninsulated flooring in the shed/outbuilding.
This could mean that the floor is at 'true earth' potential - bit like being outside.
This could be dangerous if there was a loss of supply neutral, (or a high resistance joint on the supply neutral), as all bonded metalwork will rise in potential compared to true earth.

So, it's not a case of myths, it's a case of people only grasping bits of information and repeating them.:)

There isn't a 'yes you can' or a 'no you can't' - it's up to you, the designer/electrician, to make your decision based on the characteristics of the installation and the outbuilding.

Happy Days;)
 
Your not exporting anything, but rather Extending an Extraneous Conductive Zone, in cases where there are extraneous conductive parts at outbuildings, whether it be TN-S or TNC-S (PME)....

As for uninsulated floors, well there's not much difference in this instance, to housing built prior to i think the 60's where there was no slab damp proofing layer required or laid under solid concrete floor slabs and with tiled finishes...

As for the dangers, the same dangers exist at any PME installation, but the chances of that ever happening is to say the very least is slim indeed.... If there was to be a catastrophic neutral breakdown on a PME supply line, the chances are, it will be tripped out of service by the DNOs protective devices at the supply source. In truth, there are as many myths to PME neutral failures, as to being able to extend a PME system!!!
 
Last edited by a moderator:
Your not exporting anything, but rather Extending an Extraneous Conductive Zone, in cases where there are extraneous conductive parts at outbuildings, whether it be TN-S or TNC-S (PME)....

As for uninsulated floors, well there's not much difference in this instance, to housing built prior to i think the 60's where there was no slab damp proofing layer required or laid under solid concrete floor slabs and with tiled finishes...

As for the dangers, the same dangers exist at any PME installation, but the chances of that ever happening is to say the very least is slim indeed.... If there was to be a catastrophic neutral breakdown on a PME supply line, the chances are, it will be tripped out of service by the DNOs protective devices at the supply source. In truth, there are as many myths to PME neutral failures, as to being able to extend a PME system!!!

Being an 'Engineer', perhaps you could explain how a broken neutral, or (more likely), a high resistance neutral joint in the street outside your property would trip a DNO protective device.

Let's take a scenario:

If you had a rising copper water main in your outbuilding and this was bonded back to the MET in 10mm to satisfy PME supply conditions.
If, for whatever reason, you then lost the supply neutral (which is your earth), or the impedance of this neutral rose undetected due to a dodgy joint etc, then some of the 'normal operating current' from your property (and possibly some of your neighbours' as well), will find an alternative path back to the transformer.

This path could be the rising main in your outbuilding, which would mean that the 'rising main' and any other metalwork will rise in potential, depending on the amount of current taking this path. (don't forget, the RCD won't trip).

If this happens and you touch any of this metalwork in the outbuilding, you should be ok, because it's all bonded together, so all at the same potential, BUT, if you are in contact with 'true earth' (e.g. through the floor) then you could get a shock.

This could also happen under normal operating conditions, although the current taking this alternative path would be very low, unless you had a fantasticly low Ra on the rising water main.

Like I said in my post, it's up to the designer/installer to weigh up the pros and cons of running earths to seperate buildings - it all depends on the circumstances.:D
 
Being an 'Engineer', perhaps you could explain how a broken neutral, or (more likely), a high resistance neutral joint in the street outside your property would trip a DNO protective device.

Let's take a scenario:

If you had a rising copper water main in your outbuilding and this was bonded back to the MET in 10mm to satisfy PME supply conditions.
If, for whatever reason, you then lost the supply neutral (which is your earth), or the impedance of this neutral rose undetected due to a dodgy joint etc, then some of the 'normal operating current' from your property (and possibly some of your neighbours' as well), will find an alternative path back to the transformer.

This path could be the rising main in your outbuilding, which would mean that the 'rising main' and any other metalwork will rise in potential, depending on the amount of current taking this path. (don't forget, the RCD won't trip).

If this happens and you touch any of this metalwork in the outbuilding, you should be ok, because it's all bonded together, so all at the same potential, BUT, if you are in contact with 'true earth' (e.g. through the floor) then you could get a shock.

This could also happen under normal operating conditions, although the current taking this alternative path would be very low, unless you had a fantastically low Ra on the rising water main.

Like I said in my post, it's up to the designer/installer to weigh up the pros and cons of running earths to separate buildings - it all depends on the circumstances.:D



DNOs tend to take great care in there PME supplies, employing pretty sophisticated monitoring/protection relay devices. I will in due course enquire what such monitoring devices are normally provided, when i next speak to my DNO friend (Regional Manager) and relay that information back to this thread.... I would imagine it would be in the form of a VIP module (multi function monitoring/protection relay) set to the individual parameters of the system it's connected too..

Don't knock a good rod system, lol!!! ...Depending on it's installation and the type of ground soil, it's not particularly uncommon to be re-paid with a sub 1ohm or thereabouts readings. But very doubtful with the use of these now common short thin rods... And would be totally pointless from an economical view point for a domestic outbuilding/shed!! ...lol!!!!

Yes i do agree with you, it most certainly is upto the designer/installer to decide what is the best solution/method of running PME, or any other type of electrical supply to out buildings.
 
New posts

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock