M
Maff
When installing a 'garage cu' adjacent to the main ccu to accomadate an RCD for connecting a TL inverter, what cable size would you use to link the cu's , less than 400mm run
How & where you intend connecting to the existing install will govern what size cable you will need to use i.e what rating is the overcurrent protection at the point you are connecting to....is it the suppliers fuse or an MCB etc??jWhen installing a 'garage cu' adjacent to the main ccu to accomadate an RCD for connecting a TL inverter, what cable size would you use to link the cu's , less than 400mm run
Fit a Double Pole RCD, as you said on a previous post it is transformless type Invertor so you need a B type RCD.
it a 2.6KWp system. We are doing a ccu change, so was going to put in an isolator switch, its an SMA inverter which according to its specs says a type A RCD, from reading the DTI guide I got the impression that a, you have to oversize the cabling, b) you must keep the ac supply seperate from any other circuits
You can probably miss out the henley; just take both cables from the output of the isolator. The second cable only needs to be 4mm/6mm which is likely to fit in the terminals with a 25mm. It is protected from fault by the DNO fuse (unless the DNO has specified a minimum cross sect area).
The SMA installation instructions do NOT require a rcd. They say if an rcd is required then it must be a minimum of 100mA. And type a rcd is fine for SMA TLs.
Also, as there is only the one device on the circuit, the inverter, then there is no need to protect against overload from the mains side of it, only fault.
Regards
Bruce[/QUOTE
Then they must have another form of separation other than a transformer.
If you don't fit an RCD B type as fault protection then you have to install an Inverter that will not allow DC fault currents back into the AC side.
If the SMA Inverters are transformerless, and do not need a Type B RCD protection, then they must have either another form of separation, or the capability of not to allowing those DC fault currents to pass through.
If the SMA Inverters are transformerless, and do not need a Type B RCD protection, then they must have either another form of separation, or the capability of not to allowing those DC fault currents to pass through.
Seems there are a lot of practices within the PV industry that is taken directly from Germany, another is the rod procedure for earthing an array frame if the earthing system is TNC-S. Here in the UK there is no problem with our stable PME system and I personally can not see an advantage of fitting a rod when you have a much more stable earthing system available to you.
Is the German PME system less stable than ours? I didn't know that.
The grey area with PME/PV systems is a nightmare. I can see both sides of the argument but currently we are advised to install a seperate earth rod and it's what we've been doing until we get told otherwise.
Many years ago when the Electrical safety Regulations were in force it was advised to contact the DNO and seek permission, but today if you called the DNO to ask they would most likely be incredulous about your request.
The issue is, as I see it, that in the event of a fault which took the neutral out at supply, the array would become 'live' and potentially lethal to anyone working outside of the property.
Sure - But isnt PME "multiple earth" so the neutral conductor is earthed in stages along the line from the supply? But if broken neutral in CU then is a problem
[h=2]Re: additional cu cable size[/h]
The issue is, as I see it, that in the event of a fault which took the neutral out at supply, the array would become 'live' and potentially lethal to anyone working outside of the property.