So a customer changed his own stat and wired it wrong and blew 3/4 fuses. Then heating was stuck on so I changed the programmer and this resolved the problem so I think the short circuit had damaged programmer.
Now 5 days later the the hot water isn’t heating haven’t been yet. All I can guess is the cylinder stat or zone valve could have problem.

Any ideas?

Thanks
 
Yes, go there with the proper test equipment and identify the fault.
How familiar are you with heating systems, isit a y or splan?
 
Then heating was stuck on so I changed the programmer and this resolved the problem so I think the short circuit had damaged programmer.

Did you test it first before replacing it or was it a bit of guesswork?

How do you think a short circuit may have caused damage to the programmer?
 
The live at room stat was permanently live regardless of the position on the programmer. The programmer was always calling for heating even when In off position. So I tried a new Drayton programmer and heating was fine.

Thanks
 
Last edited:
My heating experience isn’t huge. It’s an S plan.
 
I have had many programmers welded on by short circuits
 
So I’m wondering if that could affect cylinder stat or zone valve possibly?

Thanks
 
You need to do some live testing.

Is power going to the stat when calling for heat?

Is power coming back from stat when cold?

Does manually opening the zone valve bring it on?


A major short circuit may have damaged more than the programmer, but you need to test thoroughly rather than playing parts bingo.

Do you know what the customer had done? If he wired the stat wrong, I would expect this stat to bear the brunt of any fault, not the programmer some distance away….
 
  • Like
Reactions: nicebutdim and DPG
Did you change the programmer like for like? The base is sort of standard, but the wiring connections vary.
 
You need to do some live testing.

Is power going to the stat when calling for heat?

Is power coming back from stat when cold?

Does manually opening the zone valve bring it on?


A major short circuit may have damaged more than the programmer, but you need to test thoroughly rather than playing parts bingo.

Do you know what the customer had done? If he wired the stat wrong, I would expect this stat to bear the brunt of any fault, not the programmer some distance away….
I suspected the programmer as the room stat was still live when the programmer was off.

I will check those things you said.

Thanks
 
  • Like
Reactions: Jim_e_Jib
Seem the hot water 2 port valve is also faulty. It moves accross but it doesn't make the orange become live so the boiler isn't firing up. So hopefully this is it fixed once I get hold of a new valve.

thanks
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dorset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Central heating fault.
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Dave123,
Last reply from
Dave123,
Replies
10
Views
1,746

Advert