Chandelier bulbs keep blowing | on ElectriciansForums

Discuss Chandelier bulbs keep blowing in the Australia area at ElectriciansForums.net

S

Stefone

Hi everybody

Every time I went to my grandparents their chandelier had around 4 out of the 10 bulbs that had blown, this would happen after a couple of weeks of being replaced and it would alternate between the 10 sockets. It is on a 10amp type b breaker and there has been no issue with this since the fault started occurring and has not been tripping and I am sure they are not exceeding the maximum load wattage for that circuit. The bulbs they buy are from the local wholesalers and aren't particularly cheap, the chandelier is connected to a dimmer but the bulbs are dimmerble, the sockets are metal so should be able to take a higher wattage then say the plastic type. I recently replaced all the bulbs with the long life energy saving type which are dimmerble and this seems to have made the problem worse, there was some water damage to the ceiling some time ago but I cannot see how this would cause this particular fault, could somebody please please enlighten me, excuse the pun
 
the water damage could have caused a problem with connections in the ceiling rose. a loose connection could be the cause. bad contacts on the lampholders, could be anything in that vein. i would suggest calling a sparks in. there may be an underlying problem with the installation.
 
Thanks, will check the connections in the ceiling Rose, could be a loose termination in the neutral, I'm j.I.b and don't normally mess around with domestic and the ceiling is really high plus it's a 2 man job to take down and reinstall which was why I was avoiding that route, the fact that the bulbs that are blowing keep on alternating brought me to the conclusion that it's not the connection to the lamp holders as 1 bulb may work for 6 months but once it's replaced it will suddenly blow and then after being replaced may work for a few months? Will just have to rent a decent ladder check the connections in the Rose, complete a ze and failing that get another pair of hands and re-wire chandelier ;-(
 
The only reasons I have ever found for bulbs blowing frequently are:
1. Cheap bulbs.
2. High mains voltage.
3. The lamps are old and reached the end of their life.
Never found the problem to be loose connection but it could cause the problem.
If it was loose connection the customer usually notices the lamps flashing.
 
Last edited:
For removal advice for removing chandaliers can only encourage you to use Trotter Trading Company world wide reputation for chandalier work especially in country houses their training video can be found at all reputable video shops.

On a personal note involved with a lot of Nursing Homes with large quantities of chandaliers have changed them to 3w LED lamps and they have been fantastic. One had 36 lamps in and prior to changing to LED they were using low energy really made the chandalier look cheap and nasty lots of plastic balls. Lights uses 24/7 because of doing that one light fitting have now been involved with changing over 1200 lamps. Im happy and the client is very happy paid for inself in energy savings already.
 
If it's an old Chandelier it could simply be due to poor / weak springs on the contact pins in the Lampholders. Over the years with heating / cooling they can deteriorate & it turns into a vicious circle, you get poor Pin to Bulb contact which creates localised heating at the Filament terminals & kills the bulb.
 
Last edited by a moderator:

Reply to Chandelier bulbs keep blowing in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
UPDATE, after contacting Paypal, uploading all the emails and evidence the sending the transformer back I have now received a full refund...
Replies
6
Views
2K
It will last longer more then 4-5 weeks.or you have overloaded the dimmer.
Replies
7
Views
3K
  • Question
By all means do that but personally I would wait. Its an intermittent fault after it occurs more than once. You are likely correct that the kettle...
Replies
9
Views
2K
  • Question
Are all the other lights on the circuit switched on or off?
Replies
12
Views
7K
Octopus
O
Mini AC Leakage Current Meter - MP780050 looks to me to be the same as the first two but only £40 at CPC.Farnell I have ordered one rather than...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks