I have a few installs coming up where I need to upgrade cu's and want to install isolators between DNO service head and new consumer units. I have only ever fitted before to twin supply houses on off peak storage heating and was under the impression that a straight enclosure with a 100A DP main switch would be good enough. But DNO have just told me that they also require over-current protection. On two supply i usually use a Hager 4P switch and 2 x 63A MCB's for feed tails but could I use a 100A dp and a separate MCB in enclosure on Brown tail ? or does anyone use easily sourced different equipment?

Thanks,
 
This is the standard bit of domestic kit for fused isolation for tails. Readily available and easy to use with tails.
You don't want to be using an upfront MCB for the discrimination issues involved which can result in possible non compliance with the regs.


CGMSF100.JPG
 
But of course from January we will all love using the Amendment 3 all metal switch fuses!:(
Wylex all metal Switch Fuse.jpg

Joking aside I would echo Andy78 do not use an MCB, use a Switch fuse.
The DNO usually specify overcurrent/fault protection for longer tails runs (often over 3m), but should generally be happy with just an isolator for a short run to a CU.
 
Hey all,

I have a few installs coming up where I need to upgrade cu's and want to install isolators between DNO service head and new consumer units. I have only ever fitted before to twin supply houses on off peak storage heating and was under the impression that a straight enclosure with a 100A DP main switch would be good enough. But DNO have just told me that they also require over-current protection. On two supply i usually use a Hager 4P switch and 2 x 63A MCB's for feed tails but could I use a 100A dp and a separate MCB in enclosure on Brown tail ? or does anyone use easily sourced different equipment?

Thanks,

Why??? What is their reason?
 
Hi DNO is Jersey Electricity Co and usually they like isolator before cu as they say good practice but if I am having homes on 100A single phase supplies there seems no benefit to use 63A to protect the line tail as you can't then take your higher supply current so counter productive. If I could work out how to post up a pic or two I could show you what is usually fitted by others.
 
That must be new. I don't remember the JEC requiring that before.

Although ESB requires a 63A MCB for meter tails exceeding 3 metres. (Not a fan of this for reasons of discrimination/selectivity mentioned.)
 
Just picked up a 100A Wylex all metal switch fuse but it's like £70 ! & the size of the cu ! Meter tails are approx a foot max so don't know what's going on there. Think I'll call them again as it's nuts
 
The DNO should be happy with that, the customer wont be when a short circuit takes out their main supply.
The DNO asks for overcurrent protection so it does not have to be discrimination from the DNO fuse.
 
I don't get how else I'm going to get overcurrent protection without the usual Mcb route as used for comfort heat boards / isolators, spoke to them & they say Mcbs are usual requirement and at 63A. Or should DNO fuse be the only required overcurrent protection ?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Soulsurfer

Arms
-
Joined
Location
Channel Islands
Business Name
M.B.S ELECTRICAL

Thread Information

Title
Domestic meter tail isolator
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
38
Unsolved
--

Advert

Thread statistics

Created
Soulsurfer,
Last reply from
Paulgwat,
Replies
38
Views
11,327

Advert

Back
Top