Hi chaps,

This may have been asked before but i cant seem to find it when searching so im sorry if someone easily finds it.

Im currently carrying out a EICR at a commercial premises and the water is bonded from a sub DB and not the MET, its something that i understand needs to be noted but is it something that needs to be coded? If so what code?

Thanks
 
I think reg 542.4.1 applies : "in every installation a met shall be provided to connect the following to the earthing conductor - CPCs - protective bonding conductors ... etc"

My 20p worth : the existing arrangement is not in accord with 542.4.1 and so I would give it a C3, as it is not unsafe (for you to confirm with testing?) but it would be an improvement to comply with regulations.

I'm not expert in this one, and others please feel free to jump in :)
 
I say that as long as the water pipe (if extraneous) is connected to the MET by conductors that comply along the whole route with the requirements of protective bonding conductors, it doesn't matter if they go via one or more other terminals.

542.4.1 doesn't say that all CPCs, protective bonding conductors, etc. have to be connected directly to the MET. In fact most CPCs won't be connected directly to the MET.
 
Hi chaps,

This may have been asked before but i cant seem to find it when searching so im sorry if someone easily finds it.

Im currently carrying out a EICR at a commercial premises and the water is bonded from a sub DB and not the MET, its something that i understand needs to be noted but is it something that needs to be coded? If so what code?

Thanks
Hi akwoody2 have the Mods got your profile correct because you are down as DIY, I have to ask because if you are actually a DIY Member do you think you should be doing EICRs?
 
Hi akwoody2 have the Mods got your profile correct because you are down as DIY, I have to ask because if you are actually a DIY Member do you think you should be doing EICRs?

Hi Pete,

I'm a fully qualified electrician, not to sure why I'm down as DIY. Maybe something to do with me not putting my qualifications in yet?

Do you have an opinion on the bonding to the water?
 
Hi Pete,

I'm a fully qualified electrician, not to sure why I'm down as DIY. Maybe something to do with me not putting my qualifications in yet?

Do you have an opinion on the bonding to the water?
Well it is connected to the MET in a round about way, without seeing the job it's quite hard to form an opinion, as for your profile, best you get it updated, the wrong,or no info can lead to incorrect or sometime abusive answers, the non filling out of profile info is a pet hate of mine, I have posted before requesting correct profile info is a must, but quite rightly you can't make people provide info if they don't want to.
 
Well it is connected to the MET in a round about way, without seeing the job it's quite hard to form an opinion, as for your profile, best you get it updated, the wrong,or no info can lead to incorrect or sometime abusive answers, the non filling out of profile info is a pet hate of mine, I have posted before requesting correct profile info is a must, but quite rightly you can't make people provide info if they don't want to.


I'll get it done for you tonight Pete!
 
So is the amour acting as a cpc and bonding conductor

Well if you read the post its obvious it is being used as that at the minute! But incorrectly so, 16mm 4c has steel equivalent of 72mm which in terms of copper equivalent is inaquate in terms of being <10mm. I would back you up in a C2 observation on that observation.
 
Well if you read the post its obvious it is being used as that at the minute! But incorrectly so, 16mm 4c has steel equivalent of 72mm which in terms of copper equivalent is inaquate in terms of being <10mm. I would back you up in a C2 observation on that observation.

Thanks. Out of interest how did you get to it being the equivalent of <10mm?
 
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?
 
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?

I'd run it back to the MET as it's not actually that far away
 
Last edited:
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?

So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?
 
So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?
Because people don't understand that just because the armour has a large csa it isn't necessarily adequate to support bonding. Rule of thumb times your bonding size by 8 to get the required size of armour, GN8 has all the info. If you have a four core cable less than 50.0 it will be inadequate to support the minimum size of 10.0 bonding
 
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?

The cpc also needs upgrading for the 100a supply to the sub board
 
Putting on my student's tin hat, I'll give it a bash :

For bonding we are concerned about touch voltages and so the path must be comparable to the resistance of Cu and so we use resistivity ratios (>8). For use as CPC we use the adiabatic eqn and its k factors that include temp rise and thermal capacity of the materials. This gives a reduced steel requirement compared with bonding calcs and so SWA armour is often ok for CPC but not for bonding.
 
So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?

Because CPC size is calculated by the adiabatic equation and not by the equivalent conductivity method used for bonding. the CPC only has t carry fault current for a specified time which is limited by the fault protection device and so can be a lot smaller than the bonding conductor required on TNCS.
 

Reply to EICR question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
772
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
842
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
Actually I hadn't. I've taken on board everyone's comments, thank you.
2
Replies
26
Views
8K
  • Question
I don't normally deal with them, but 702.415.2 is worth checking out.
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks