Hi All. Hope someone can help here as I'm confused with all the info floating around all over the net.

Our shower blew its PRD last night and we were going to buy a nice new upgrade.

Having removed the cover the get the rating we discovered a 9.5kw HOWEVER, the shower is connected with (old red & black) 6mm T&E with a 32A MCB switch in the consumer unit. No idea what rating the pull switch is.

My understating is that a 9.5kw should be running with 10mm and a 45A MCB with a 45A pull switch??

The shower has seemingly been running like this for 6 years since the bathroom was done with no issues... but as above, it seems wrong and am surprised we havent burnt the house down.

Work was all done and tested and signed off, no bodging as far as I was aware but obvs I'm now questioning that!

If it helps, the cable runs from under the stairs, around 8-10 meters to the pull switch, through floor and standard stud walling.

Any advise here would be fantastic before I get a sparky in as I would like to understand this.

Many Thanks in advance
 
9.5 kW (40A) is just about the limit for 6.0mm cable as long as the cable is not installed in insulation. a 32A MCB will stand 40A for a good while before it trips. showers tend to be on for 10 -15 minutes , such short duration is OK for bot cable and MCB. that's why you've had no problems. just be aware that if you uprate the shower, that's when you'll need 10mm cable.
 
  • Like
Reactions: DPG and Rpa07
The shower the other half wants is a bit less at 9kw.

If I asked a sparky to replace my MCB for maybe a 40A and fit the new 9kw Shower, A, do you think that's suitable and would suffice & B, would a sparky be happy doing that or would they insist on fitting the 10mm?

Id rather be as safe as I can with it, as you have said it' only on for 10-20min a time so heat build up isn' a problem I don't think, but I'd rather not have to add hundreds to my bill by having to replace the cable
 
  • Optimistic
Reactions: 1 person
the shower circuit cable is it RCD protected if not by changing the shower it needs to be done.
 
you must remember not all showers are the same for water inlet
and cable entry .
 
who's make of shower is installed now ?
 
If I asked a sparky to replace my MCB for maybe a 40A and fit the new 9kw Shower, A, do you think that's suitable
Why do you need to do this??.
Has the MCB ever tripped with a larger load of 9.5Kw?
 
My shower is a 10kW and is on a 6mm cable (yes I know). It's a short run and is not in insulation and the cable barely gets warm. Not saying it's right, just thought I'd try and stop you thinking your house will catch fire.

It's more likely to catch fire from loose connections, etc. to be honest. Sorry, that's not helping now is it :eek::)
 
9.5 kw divided 230=41 amps
 
  • Like
Reactions: DPG
9.5kW divided by 240 = 39.6 Amps.
 
Measure your supply - see what it is.
 
It' a Triton at min, want a Mira replacement now. New Mira is a 9kw.

As for entry points new one has a rear and will offer it up to see if it cover old mounting holes sufficiently.

CU is, I believe by looking at labels, 230V.

Measured the the distance. 8 meters from CU to pull switch, 1 meter then to shower. That' rounded up too. 10 meters for whole distance Absolute maximum.

If only it was already 10mm :(
 
that 6mm willl be fie and so will the 32A MCB. your nominal supply is 230V (blame them brussels sprouts for this) but it's still closer to 240V in real world. the worst thing thart can happen is the 32A MCB tripping if teenage daughters use the shower for their usual 3 hours. as DPG said, the main danger with showers is limp wristed electricians that can't tighten terminals correctly. get your new shower installed and ask the electrician to check the connections in the isolator. if he/she insists on a 10mm cable, they're fishing for work. get someone more honest.
 
  • Like
Reactions: Des 56 and Rpa07
Thanks!

Exactly what I was afraid of, getting a sparky in, No offence to any on here at all, but being told you need a full rewire for the shower and what that entails when a new like for like will go for another 6 years for sake of a "job" and to line their pockets.

Plenty of good advice and thanks very much guys. It's a mine field with much debate I can tell. It was all signed off and certified when the bathroom was done so im going to go with a like for like replacement I can do myself with no alterations.

The Mira is out you'l be pleased to know buzzlightyear! Entry points and mounting completely different to the Triton :thumbsup:
 
The Mira is out you'l be pleased to know buzzlightyear! Entry points and mounting completely different to the Triton :thumbsup:
good man,
the reason is said about the Triton UK made .had a shower went down on the customer, I turned out met the engineer from triton he used to work for Mira. he told me the stuff made for them is c**P.
 
i don't like showers anyway. bloody useless objects. water gets in your single malt and makes your smoke and your book soggy. give me a bath any time. whisky on 1 side, ashtray on the other.
 
  • Like
Reactions: buzzlightyear

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Electric Shower Help!!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
David Burgess,
Last reply from
telectrix,
Replies
19
Views
2,268

Advert