Does a new cable that’s supply a garage need to rcd protected at the consumer unit inside or can it be supplied off the non rcd side of the
consumer unit?

The garage will have a rcd consumer unit inside.

Any help would be appreciated. Thanks
 
Depends on the cable type and how it is run.

If it is SWA then the earthed armour means no need for RCD protection for that cable.

Flexishield is a similar idea, but the aluminium foil layer has a modest limit for any MCB so it can safely disconnect.

If it is any other cable type it has to be such that it can't realistically be penetrated by accident, so not buried less than 50mm from any surface, and where outside either protected by duct/conduit or run in a manner where it is safe from any realistic risk of damage from gardening activities, etc.
 
  • Like
Reactions: loz2754
Depends on the cable type and how it is run.

If it is SWA then the earthed armour means no need for RCD protection for that cable.

Flexishield is a similar idea, but the aluminium foil layer has a modest limit for any MCB so it can safely disconnect.

If it is any other cable type it has to be such that it can't realistically be penetrated by accident, so not buried less than 50mm from any surface, and where outside either protected by duct/conduit or run in a manner where it is safe from any realistic risk of damage from gardening activities, etc.
Thank you, I thought the same but just making sure ??
 
unless it's TT earthing. then the cable will need RCD for fault protection.
 
As @telectrix points out, if the supply is TT then you need some sort of RCD as a cable fault is unlikely clear otherwise. But in that case you ought not to have a non-RCD side in the first place!
 
  • Like
Reactions: loz2754
Just to add, you might have a non-RCD side (no 30mA instant RCD) but with a 100mA delay RCD incomer in a TT system.

So yes, it could be a little more complicated...
 
  • Like
Reactions: nicebutdim
Just to add, you might have a non-RCD side (no 30mA instant RCD) but with a 100mA delay RCD incomer in a TT system.

So yes, it could be a little more complicated...

Was just about to ask if upfront 100mA time delayed RCD would be considered suitable protection on a TT installation?
 
Was just about to ask if upfront 100mA time delayed RCD would be considered suitable protection on a TT installation?
It would be OK for SWA cables, etc, that don't normally need RCD, as it would allow a cable fault to disconnect the supply even though the TT earth is not low enough impedance to trip the sub-main OCPD.

But it would not allow non-shielded cable types in vulnerable locations as if you nailed it the resulting metalwork would be capable of giving a fatal shock before the 100mA delay RCD disconnects.
 
  • Like
Reactions: nicebutdim
Wouldn't the additional protection requirement then apply after the 100mA delay RCD, therefore additional 30mA RCD's will be required.
 
  • Like
Reactions: loz2754
Wouldn't the additional protection requirement then apply after the 100mA delay RCD, therefore additional 30mA RCD's will be required.

To be specific, I'd wondered if 100mA was suitable as upfront protection, with circuits from garage board being protected by 30mA RCCB.



Let's assume a TT installation where all circuits are afforded 30mA protected by RCBOs, with upfront time delayed 100mA RCCB providing additional protection. Would it be better to:

A) Protect armoured run to via MCB, with RCBO board at outbuilding end.

or

B) Protect armoured run with RCBO and use MCB protection at outbuilding?

My thinking leans towards the former, but I have insufficient knowledge to suggest that either method would be a better set up.
 
Let's assume a TT installation where all circuits are afforded 30mA protected by RCBOs, with upfront time delayed 100mA RCCB providing additional protection. Would it be better to:

A) Protect armoured run to via MCB, with RCBO board at outbuilding end.

or

B) Protect armoured run with RCBO and use MCB protection at outbuilding?
The OP said they have a garage CU with RCD there, so I would be going for a MCB (or switch-fuse) to feed SWA so only the one 30mA "additional protection" RCD to trip/reset, and near where it is used.

Also slightly less leakage current as no long run of SWA on it, though I suspect that is trivial, probably only a few hundred pF per meter of SWA.

If the garage CU was a RCBO board then a leak tripping the sockets won't plunge it in to darkness by taking out the lights, though a hard fault would still probably take out the MCB feeding it (due to the poor selectivty of cascaded MCBs).
 
Last edited:
  • Like
Reactions: nicebutdim
What I would not want is the garage feed coming off the RCD-side of my home CU, as any fault out there (which is more likely due to water, etc) is going to take out my other home circuits.

Hypothetically, as I have an all-RCBO board. Also I'm in a 3rd floor flat so a garage supply is a bit unlikely! :)
 
  • Like
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Garage supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Mabro22,
Last reply from
pc1966,
Replies
11
Views
4,996

Advert