Does a new cable that’s supply a garage need to rcd protected at the consumer unit inside or can it be supplied off the non rcd side of the
consumer unit?

The garage will have a rcd consumer unit inside.

Any help would be appreciated. Thanks
 
Depends on the cable type and how it is run.

If it is SWA then the earthed armour means no need for RCD protection for that cable.

Flexishield is a similar idea, but the aluminium foil layer has a modest limit for any MCB so it can safely disconnect.

If it is any other cable type it has to be such that it can't realistically be penetrated by accident, so not buried less than 50mm from any surface, and where outside either protected by duct/conduit or run in a manner where it is safe from any realistic risk of damage from gardening activities, etc.
 
Depends on the cable type and how it is run.

If it is SWA then the earthed armour means no need for RCD protection for that cable.

Flexishield is a similar idea, but the aluminium foil layer has a modest limit for any MCB so it can safely disconnect.

If it is any other cable type it has to be such that it can't realistically be penetrated by accident, so not buried less than 50mm from any surface, and where outside either protected by duct/conduit or run in a manner where it is safe from any realistic risk of damage from gardening activities, etc.
Thank you, I thought the same but just making sure ??
 
Just to add, you might have a non-RCD side (no 30mA instant RCD) but with a 100mA delay RCD incomer in a TT system.

So yes, it could be a little more complicated...
 
Just to add, you might have a non-RCD side (no 30mA instant RCD) but with a 100mA delay RCD incomer in a TT system.

So yes, it could be a little more complicated...

Was just about to ask if upfront 100mA time delayed RCD would be considered suitable protection on a TT installation?
 
Was just about to ask if upfront 100mA time delayed RCD would be considered suitable protection on a TT installation?
It would be OK for SWA cables, etc, that don't normally need RCD, as it would allow a cable fault to disconnect the supply even though the TT earth is not low enough impedance to trip the sub-main OCPD.

But it would not allow non-shielded cable types in vulnerable locations as if you nailed it the resulting metalwork would be capable of giving a fatal shock before the 100mA delay RCD disconnects.
 
Wouldn't the additional protection requirement then apply after the 100mA delay RCD, therefore additional 30mA RCD's will be required.

To be specific, I'd wondered if 100mA was suitable as upfront protection, with circuits from garage board being protected by 30mA RCCB.



Let's assume a TT installation where all circuits are afforded 30mA protected by RCBOs, with upfront time delayed 100mA RCCB providing additional protection. Would it be better to:

A) Protect armoured run to via MCB, with RCBO board at outbuilding end.

or

B) Protect armoured run with RCBO and use MCB protection at outbuilding?

My thinking leans towards the former, but I have insufficient knowledge to suggest that either method would be a better set up.
 
Let's assume a TT installation where all circuits are afforded 30mA protected by RCBOs, with upfront time delayed 100mA RCCB providing additional protection. Would it be better to:

A) Protect armoured run to via MCB, with RCBO board at outbuilding end.

or

B) Protect armoured run with RCBO and use MCB protection at outbuilding?
The OP said they have a garage CU with RCD there, so I would be going for a MCB (or switch-fuse) to feed SWA so only the one 30mA "additional protection" RCD to trip/reset, and near where it is used.

Also slightly less leakage current as no long run of SWA on it, though I suspect that is trivial, probably only a few hundred pF per meter of SWA.

If the garage CU was a RCBO board then a leak tripping the sockets won't plunge it in to darkness by taking out the lights, though a hard fault would still probably take out the MCB feeding it (due to the poor selectivty of cascaded MCBs).
 
Last edited:
What I would not want is the garage feed coming off the RCD-side of my home CU, as any fault out there (which is more likely due to water, etc) is going to take out my other home circuits.

Hypothetically, as I have an all-RCBO board. Also I'm in a 3rd floor flat so a garage supply is a bit unlikely! :)
 

Reply to Garage supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock