I've bought a digital thermostat to replace and old manual honeywell that's in a bit of a bad way.

I've open both up to check the wiring but the new digital doesnt have an earth. I don't want to start messing with them until I'm sure where it should be placed. I've attached some photos to help.

Any advice would be much appreciated.

14748087060101577565735.jpg

14748087284821360408914.jpg
 
Hi there,

Thanks for the help,

I've inserted all wires into the same connections on the new thermo but the display will not turn on at all? any ideas on this one?

Thank in advance!
 
Check the wiring diagram for the new stat as they are not necessarily the same as the old one. The old stat also would not have needed a neutral to function, the new one does. Is the neutral definitely connected at the other end.
 
Hi,i may have missed a bit,but what is it switching?

On occasion,it's not a floor standing Glow worm...

The original may be 10A switching,dependant on type of load,and the new one is rated at 3A.

Probably worrying about nothing...unless you have 1960's electric UFH :)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Installing digital thermostat
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
orange,
Last reply from
PEG,
Replies
5
Views
1,649

Advert

Back
Top