S
stevie2011
On a domestic install a plumber has hooked up his boiler to the mains and then run a flex probably longer than 8 meters underneath floorboards to his thermostat. I'm doing the rewire, but this had happened while i was away on other things, i'd told him this wasnt good practice and needs to be a 3 core and earth flat. As far as I've been looking the regs are vague about flex to fixed appliances, but through my experience (which has been mostly lighting systems install) we'd never used flex in lengths more than a meter, has anyone got any answers? because i can't actually think of a logical safety reason why we'd never do this.
Nothing in the regs about using flex instead of T&E. As far as I can see, you could wire a whole circuit in it, might be a bit expensive though! It should still be clipped or otherwise secured though.
Current carrying capacities & volt drop are different for cables with flexible conducters (Table 4F3A). That would have to be considered.
as long as he's got enough cores and uses the green/yellow as cpc...........
thanks guys, yeah makes sense, its no more than 3 amps anyway, I can't remember if he said 0.75 or 1 mm but i'm sure it will be alright. I guess i'm just over thinking (which i'm trying not to do) because this is the first job im solely responsible for and i think this one will be inspected by the NIC. The plumber probably lashed it in, so I'd better make sure its picked up off the ground. Panic over!
How many cores are in the flex and is one of them being used as earth / CPC?
sounds OK then. even if the stat does not require earthing, you need a cpc in the cable.
when i was training i was always told, as electricians we protect our cables, so yeah, it definitely needs an earth cable connected to earth so if a hungry mouse gets at it or something we get automatic disconnection of supply.
makes me think of the old school boy error of not joining the earths at double insulated light fittings, which means the continuity of cpc gets lost. Funny how common that is, i saw that again recently on a maintenance job, anyway I'm trailing off topic here!
Thanks for your help guys.
long flex for boiler thermostat under floors
stevie2011,
Elmer BeFuddled,