stevie2011

On a domestic install a plumber has hooked up his boiler to the mains and then run a flex probably longer than 8 meters underneath floorboards to his thermostat. I'm doing the rewire, but this had happened while i was away on other things, i'd told him this wasnt good practice and needs to be a 3 core and earth flat. As far as I've been looking the regs are vague about flex to fixed appliances, but through my experience (which has been mostly lighting systems install) we'd never used flex in lengths more than a meter, has anyone got any answers? because i can't actually think of a logical safety reason why we'd never do this.
 
Nothing in the regs about using flex instead of T&E. As far as I can see, you could wire a whole circuit in it, might be a bit expensive though! It should still be clipped or otherwise secured though.
 
Current carrying capacities & volt drop are different for cables with flexible conducters (Table 4F3A). That would have to be considered.
 
as long as he's got enough cores and uses the green/yellow as cpc...........
 
thanks guys, yeah makes sense, its no more than 3 amps anyway, I can't remember if he said 0.75 or 1 mm but i'm sure it will be alright. I guess i'm just over thinking (which i'm trying not to do) because this is the first job im solely responsible for and i think this one will be inspected by the NIC. The plumber probably lashed it in, so I'd better make sure its picked up off the ground. Panic over!
 
On a domestic install a plumber has hooked up his boiler to the mains and then run a flex probably longer than 8 meters underneath floorboards to his thermostat. I'm doing the rewire, but this had happened while i was away on other things, i'd told him this wasnt good practice and needs to be a 3 core and earth flat. As far as I've been looking the regs are vague about flex to fixed appliances, but through my experience (which has been mostly lighting systems install) we'd never used flex in lengths more than a meter, has anyone got any answers? because i can't actually think of a logical safety reason why we'd never do this.

How many cores are in the flex and is one of them being used as earth / CPC?
 
sounds OK then. even if the stat does not require earthing, you need a cpc in the cable.
 
when i was training i was always told, as electricians we protect our cables, so yeah, it definitely needs an earth cable connected to earth so if a hungry mouse gets at it or something we get automatic disconnection of supply.

makes me think of the old school boy error of not joining the earths at double insulated light fittings, which means the continuity of cpc gets lost. Funny how common that is, i saw that again recently on a maintenance job, anyway I'm trailing off topic here!

Thanks for your help guys.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
long flex for boiler thermostat under floors
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
stevie2011,
Last reply from
Elmer BeFuddled,
Replies
18
Views
7,284

Advert

Back
Top