I know main bonding to water and gas need to be 0.05 ohms

But what about the main earthing conductor?

Does it have a maximum resistance value from MET to the CU?
 
Last edited:
In practical terms assuming you have a CU very near the MET the resistance should be almost negligible, so if Zs@DB is measured it would be well under the max Ze figures of 0.35 (TNCS) and 0.8 (TNS).
It sounds as though this question relates to a particular situation and maybe more details would help.
 
Nope.
GN3 refers to a measurement made between the cable connected to the bonding clamp, and the actual pipe. This reading to be <0.05 ohms. There is no regulation specifically mentioning a maximum resistance of any bonding conductor.
lots of sparks get this wrong. the 0.05 is as you say. absofruitly nothing to do with the resistance of the bonding conductor.
 
it's to ensure that :

1. the bonding clamp is securely connected to the metal of the pipe, not through paint.

2. wet-pants hasn't fitted clamp to a plastic pipe.seen that done a couple of times.
 
In practical terms assuming you have a CU very near the MET the resistance should be almost negligible, so if Zs@DB is measured it would be well under the max Ze figures of 0.35 (TNCS) and 0.8 (TNS).
It sounds as though this question relates to a particular situation and maybe more details would help.
Not situational I have just seen a really long 16mm earthing conductor today on a tncs a few days ago and was just wondering if it had a maximum length
 
Noting that one has to be careful to define where the MET is, according to what is connected where. E.g. if the MEB conductors terminate in the CU, the cable from the origin to the CU is not just a CPC.
 
So would it be fair to say that the main earthing conductor only runs as far as the fused switch and from there on it becomes a cpc which has to meet the max Zs requirements of the fuse in the isolator which in turn dictates its max resistance?
Maybe, maybe not:
  • It has to allow the fused-switch to meet its Zs for 5s disconnection at the end of the sub-main (as you just said).
  • It has to allow all final circuits to meet the Zs requirement.
  • It has to meet the adiabatic limit for all OCPD clearing (supply fuse & finals circuits, but obviously they will be smaller and can be ignored if supply is met)
  • And also any possible extraneous bonding on TN-C-S (which ought to be back to the MET, but if sub-main to the remote board, such bonds might well be connected there) so you might have the (typically) 10mm minimum.
If you have no reason to doubt the design, then the resistance check is basically to verify it is working as designed, so based the GN3 figure would be:
R measured <= 0.05 + expected cable R2
 
So would it be fair to say that the main earthing conductor only runs as far as the fused switch and from there on it becomes a cpc which has to meet the max Zs requirements of the fuse in the isolator which in turn dictates its max resistance?

Maybe, maybe not:
  • It has to allow the fused-switch to meet its Zs for 5s disconnection at the end of the sub-main (as you just said).
  • It has to allow all final circuits to meet the Zs requirement.
  • It has to meet the adiabatic limit for all OCPD clearing (supply fuse & finals circuits, but obviously they will be smaller and can be ignored if supply is met)
  • And also any possible extraneous bonding on TN-C-S (which ought to be back to the MET, but if sub-main to the remote board, such bonds might well be

16mm to fused isolator, then 16mm to CU
Or it might have had 16mm from the met and a separate 16mm to the isolator
 

Reply to Main Earthing conductor max resistance? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock