If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
So I've been told by the NICEIC not to use the 80% rule for max Zs (even though that's the table provided on the inside of the cert books). They want me to use the 100% values from table 41.3 in the BYB. Not a problem.

However I can't seem to find a table for the BS EN 3871 MCB's in there.

Anyone know where I can find one? Otherwise I guess I will have to apply a correction factor to the 80% values every time which would be a PITA.

Thanks
 
BS EN 3871: Superseded and Withdrawn. It was replaced with BS EN 60898
 
I think you mean on the testing sheet? Yeah, they do ask that. Older regs book, or I might have a cheat sheet somewhere. I’ll just check...

Edit: no it’s just got breakers and fuses on.
 
So I've been told by the NICEIC not to use the 80% rule for max Zs (even though that's the table provided on the inside of the cert books). They want me to use the 100% values from table 41.3 in the BYB. Not a problem.

However I can't seem to find a table for the BS EN 3871 MCB's in there.

Anyone know where I can find one? Otherwise I guess I will have to apply a correction factor to the 80% values every time which would be a PITA.

Thanks
You paysyer money and takes yer choice mate, do it as per the regulations.
 
Being somewhat pedantic if they wish you to use the values from a specific table in BS7671 and that table does not have values in it for common protective devices then I would say they need to provide you with more accurate information.
To do otherwise would be the height of unprofessionalism; for the NICEIC to apply impossible demands of people who are paying them to do a job?

Anyway Stroma produced this table at the time of the amendment that includes BS3871 (but remember it is not the table you have been asked to use!).
 

Attachments

I always thought it funny that ms Clancy wanted 100% values but then she printed the 80% values in the EIC book. A bit bizarre, sure they'll have their reasons, not die they'll be logical.
 
  • Agree
Reactions: Zdb
Being somewhat pedantic if they wish you to use the values from a specific table in BS7671 and that table does not have values in it for common protective devices then I would say they need to provide you with more accurate information.
To do otherwise would be the height of unprofessionalism; for the NICEIC to apply impossible demands of people who are paying them to do a job?

Anyway Stroma produced this table at the time of the amendment that includes BS3871 (but remember it is not the table you have been asked to use!).
I always thought it funny that ms Clancy wanted 100% values but then she printed the 80% values in the EIC book. A bit bizarre, sure they'll have their reasons, not die they'll be logical.
Emma Clancy and Logic don't compute HT
 
  • Creative
Reactions: JOURNEYMAN
100 percent zs values should be used as this is the circuit worst case scenario when operating at its maximum temperature of 70 degrees.
The printed 80 percent values are just guidance to the tester.
If the circuit is over the 80 % value given then it will be over the maximum given in the tables in bs7671 at 70 degrees.
This is the maximum zs value.
 
Anyway Stroma produced this table at the time of the amendment that includes BS3871 (but remember it is not the table you have been asked to use!).

Perfect. I think that's exactly what i was looking for.

Thanks :)
 
So I've been told by the NICEIC not to use the 80% rule for max Zs (even though that's the table provided on the inside of the cert books). They want me to use the 100% values from table 41.3 in the BYB. Not a problem.

However I can't seem to find a table for the BS EN 3871 MCB's in there.

Anyone know where I can find one? Otherwise I guess I will have to apply a correction factor to the 80% values every time which would be a PITA.

Thanks
Try dividing by 4 and multiplying by 5........100%:cool:
 
or divide by 0.8
 
  • Like
Reactions: Zdb
Divide by 0.8 is what I was doing but thanks to the table provided by @Richard Burns I don't need to anymore.
 
On the calculator on your phone, just enter the value and press +25%...
Oh isn't maths fun?
SO many ways to do your sums!
 
  • Agree
  • Like
Reactions: Rpa07 and NDG Elecs
Unlike wiring a new bathroom extractor fan (without PIR)...ok, so many ways to do it...but only one correct answer.
 
  • Funny
Reactions: Wilko
  • Agree
Reactions: Richard Burns
Is this bad math day or has inflation taken us to 105% - the first post I ignored but then @pirate carries it on.
I don’t think some members are 105% all there!
 
Is this bad math day or has inflation taken us to 105% - the first post I ignored but then @pirate carries it on.
I don’t think some members are 105% all there!

But pirate is correct Rpa.

25% of what is now 80% of the original value is the same as 20% of the 100% figure!!

Clear as mud mate!
 
But pirate is correct Rpa.

25% of what is now 80% of the original value is the same as 20% of the 100% figure!!

Clear as mud mate!
I just tried that math and was very surprised that it came out as it did!
I’ll keep quiet after apologising profusely to all offended!
Cheers@NDG Elecs
 
  • Like
Reactions: NDG Elecs
Judging off this lot, I can see some having problems with the vat man.
 
It was like 6 ways to get to the same destination - we all have our favourite route and mine is not adding 25% of the 80% value - witchcraft I tell you ‘Burn them at the stake’
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Zdb

~
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Max Zs values. (20 characters)
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Thread Tags

Tags Tags
max values

Advert

Thread statistics

Created
Zdb,
Last reply from
Rpa07,
Replies
26
Views
8,934

Advert