P

pariah66

Hi

As part of a loft conversion to my 2 (now 3) floor flat in a Victorian Terraced house I have added about a dozen 2-gang sockets, a shaving socket, and about 16 downlights to my new floor, plus swapping four pendant lights for 16 downlights in the floor below.

An electrician was installing a new consumer unit today and then I got a call from the head builder who is not onsite. He told me the electrician is concerned that the main service feed coming into the fuse/meter is only 10mm across. The electrician has apparently wired and tested everything (even though he's left the ground floor lights not working) but says we can't turn on the power in the loft as he is not confident the consumer unit will not burn out or the RCDs will be constantly tripping as the mains service cable is too thin.

The head builder told me I will probably have to upgrade my supply. He started advising me to call The National Grid (I think he means UK power networks).

I checked the main feed wire and by my measurements it looks around 12mm across. My builder was saying it should be more like 35 mm across and they'd never seen this before.

I apologise for the lack of detail but that's literally all the information I have aside from two photos of the set-up which are attached.

The reason I am posting is this all seems very light on detail. For instance I would expect a bit more calculation and maybe some figures to justify why we need to shell out many thousands potentially to upgrade the supply. The same amount of people will be living in the house, there are just likely to be a few more lights on and maybe an extra device plugged in.

Could anyone offer any advice about this? Should I just accept it, should I ask UK Power Networks about it, or should I be asking for more detail about how he came to this conclusion (and if so, what?)? Do the photos suggest what we have is obviously wrong? Any pointers would be much appreciated


cheers,
Pariah66

20190523_200455.jpg


20190523_204630.jpg
 
I have never ever came across a house or flat fed by a 35mm cable it's unheard of. 10 or 16mm is usually correct if in a flat maybe 25 if a house sometimes. Ask him for his calculations as realistically unless you have electric heating or showers there shouldn't be an issue. Do you have electric heating or shower(s)?
 
I have never ever came across a house or flat fed by a 35mm cable it's unheard of. 10 or 16mm is usually correct if in a flat maybe 25 if a house sometimes. Ask him for his calculations as realistically unless you have electric heating or showers there shouldn't be an issue. Do you have electric heating or shower(s)?
 
Who installed the consumer unit?
You do need to get the incoming set up sorted out though.
That pyro needs to be glanded into a proper enclosure and then the tails need to be upgraded.
The dno will possibly insist on the pyro being replaced.
 
You need some compression glands at least on those cables entering the board
 
Sounds like you need to get an experienced electrician involved because from what you have said and shown that is currently not the case.
 
I wonder why he didn't fill in the sticker either
 
From your picture you have several issues which need addressing and an experienced, qualified electrician would have addressed these prior to starting the works. The picture of the consumer unit clearly indicates your so called electrician has limited skills and debatable qualifications.
 
In the meantime do not touch or move any of the existing cables, especially the main incoming pyro cable.
 
Thanks everyone. The electrician just installed the consumer unit. The rest has always been like it.

Am I right that there are two issues here?

1. The pyro (what is this?) needs to be glanded, earthed and tails need to be upgraded. Who would do this, the electrician, the DNO or the electricity supplier?

2. The cables going into the consumer unit need compression glands.

In addition, so far, no-one has seen anything here which suggests I need to upgrade the feed, does anyone know what questions I should be asking this electrician or what calculations I should ask him for?

I'll provide a photo of the top of the CU in the morning as I have no lights downstairs at the moment.
 
Is it just the way the light is catching the dust or does the red insulation look damaged on the supplier side of the cut out in that second picture?
 
An electrician has not installed that consumer unit and as in #15 I would be seriously concerned about other works they have carried out.
 
  • Like
  • Agree
Reactions: Wilko and Baddegg

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New consumer unit, builder says upgrade supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
97

Advert

Thread statistics

Created
pariah66,
Last reply from
Steve000,
Replies
97
Views
10,966

Advert