Hi all,
I have a dedicated cooker circuit on a
6mm cable, 32amp mcb running to cooker switch down to connection plate.
I want to install a 1kw ( just under) oven and 6kw hob! Am I ok swapping the connection plate for a dual one and connecting together??
And if so do I run 6mm flex hob to connection plate?
And 2.5 flex oven to connection plate?
Or do I have to use 6mm cable for both
Thank you
 
Are the great debate

some will say it’s fine

some will argue the oven must be fused down to 13a
 
dual cooker outlet 2.5mm cable to each appliance.
 
  • Like
Reactions: Garymcdee
Sorry! Got fed the wrong info!!
Oven is 2.2 kW
I was thinking that 1kW was too small for an oven.

Most ovens of that rating come with a 13A plug or at least pre-installed flex these days though - so you may have to take into consideration manufacturer's instructions. Curring the plug off may cause hassle warranty wise. nothing wrong with running a socket from the connection point in that case and plugging the oven in though.
 
I was thinking that 1kW was too small for an oven.

Most ovens of that rating come with a 13A plug or at least pre-installed flex these days though - so you may have to take into consideration manufacturer's instructions. Curring the plug off may cause hassle warranty wise. nothing wrong with running a socket from the connection point in that case and plugging the oven in though.
I was thinking that 1kW was too small for an oven.

Most ovens of that rating come with a 13A plug or at least pre-installed flex these days though - so you may have to take into consideration manufacturer's instructions. Curring the plug off may cause hassle warranty wise. nothing wrong with running a socket from the connection point in that case and plugging the oven in though.
Thanks for reply, I have no plug on cooker! I need to install new cable, what size cable would you go for from hob to point and cooker to point? Am I ok putting a 2.5 t/e on cooker and 6 t/e on hob or do I need to run all 6 because on a 6mm circuit??
Thanks again
 
Thanks for reply, I have no plug on cooker! I need to install new cable, what size cable would you go for from hob to point and cooker to point? Am I ok putting a 2.5 t/e on cooker and 6 t/e on hob or do I need to run all 6 because on a 6mm circuit??
Thanks again
Personally I'd use heat resistant flex, but I'd say 2.5 to the oven is fine yes. Because the oven is a fixed load it shouldn't be possible to overload the cable long term and any direct short should easily trip the breaker before the cable suffers. (I assume it's a type B?).
 
  • Like
Reactions: Garymcdee
Dual outlet fine, I do this myself and your covered here without even applying diversity so crack on.
[automerge]1601666313[/automerge]
ps - 4mm to hob and oven good on either 1.5 or 2.5, don't forget to dress the terminations.
 
Personally I'd use heat resistant flex, but I'd say 2.5 to the oven is fine yes. Because the oven is a fixed load it shouldn't be possible to overload the cable long term and any direct short should easily trip the breaker before the cable suffers. (I assume it's a type B?).
Yes type B
Would I be ok running hob on same or would you go for 4mm t/e?

dual cooker outlet 2.5mm cable to each appliance.
dual cooker outlet 2.5mm cable to each appliance.
[automerge]1601666732[/automerge]
Yes type B
Would I be ok running hob on same or would you go for 4mm t/e?
dual cooker outlet 2.5mm cable to each
appliance.
Would that be ok even tho on a 6mm circuit
Thankyou
 
  • Like
Reactions: Garymcdee
Not really much need for a heat resistant cable when the appliances are sitting in a highly flammable normally chipboard casing :)
 
  • Like
Reactions: Garymcdee
Not really much need for a heat resistant cable when the appliances are sitting in a highly flammable normally chipboard casing :)

Fair point :) And it's rare that I see the heatproof tape installed that many of the instruction manuals mention.

But I've seen a few cables trapped between oven and hob that have been damaged by heat, and there is no tick box on my certificate for kitchen cupboard material....
 
  • Like
Reactions: stevethesparks
Fair point :) And it's rare that I see the heatproof tape installed that many of the instruction manuals mention.

But I've seen a few cables trapped between oven and hob that have been damaged by heat, and there is no tick box on my certificate for kitchen cupboard material....
Still good practice so good on you
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warrington

Thread Information

Title
Oven and hob wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
Garymcdee,
Last reply from
stevethesparks,
Replies
13
Views
8,129

Advert