Can I spur from a RCD protected ring main socket in the house to supply an RCD 2 way board in the summer house, and would it need to be fused at the socket to a spur in the main house? Thanks Alan.
As for TT its TNCS so no need. The install is a couple of sockets and a couple of lights, also there will be an oil filled rad running from a socket, at max 2kw or 9amp, with the 2 lights about 1amp, if you add the possibility of a lawn mower and strimmers, well do the math. Problem I have is the board is at the front of the house in a mid terrace, and the summer house at the rear end of the garden, about 20 metres, otherwise there is plenty of spare ways to have its own circuit, but no way getting it through without wrecking the place, which would have been the best bet.Only option is the socket at the rear of the house with a fused spur, then 20 metres of 4mm armoured to the summer house, then rcd main switch two way board for circuits inside. Correct me if I`m wrong please as I cant see any other way around it.
I agree no need to TT I was only joking. I would just fit an ordinary 63amp main switch in your 2way board as it is a complete waste of an rcd. Rcd covering an rcd?