Those KMF switch fuses arent really used for terminating SWA but you could put a metal adaptable box below each one and gland the SWA into those passing through into the KMf switch.
I don't get why people add a superfluous metal box to terminate a SWA (unless the space is required, or to turn a corner etc) when there are so many correct ways to terminate SWA cables.
 
How would you terminate SWA into a KMF switch then?
As you said they are not suitable.
I'd select a product more suited to the requirements of the job rather than botch something that isn't.

More to the point I can never workout why people do this sort of thing1751900222955.jpeg1751900039843.jpeg
 
Last edited:
Only reason I could envisage would be an original plastic consumer unit, using a metal box to get the earth… then the consumer unit being changed later to metallic
 
Only reason I could envisage would be an original plastic consumer unit, using a metal box to get the earth… then the consumer unit being changed later to metallic
Why use a metal box to terminate the earth into a plastic enclosure?

In the Metal CU I posted the CU preceeded the metal box and the white plastic conduit fitting replaced the coupling (standing on top), supposedly to cure RCD tripping problems, note the voltage between CU and add on box. 1751901624950.jpeg
 
Last edited:
If RCD is not required at this location use 3 DP B63 MCB (or as appropriate) in 3 encloseres.1751903282265.jpeg

Although I 100% agree with previous advice that fuse is more suitable, another possibility is use a CU enclosure to hold whatever devices are required, such as DP isolator, 60A fuse in holder & RCD as required for each circuit.
Add labels as appropriate about individual feeds etc.
 
Last edited:
If RCD is not required at this location use 3 DP B63 MCB (or as appropriate) in 3 encloseres.View attachment 122529

Although I 100% agree with previous advice that fuse is more suitable, another possibility is use a CU enclosure to hold whatever devices are required, such as DP isolator, 60A fuse in holder & RCD as required for each circuit.
Add labels as appropriate about individual feeds etc.
Sorry, didn't read OP correctly
 
Why use a metal box to terminate the earth into a plastic enclosure?

In the Metal CU I posted the CU preceeded the metal box and the white plastic conduit fitting replaced the coupling (standing on top), supposedly to cure RCD tripping problems, note the voltage between CU and add on box. View attachment 122526
Dont see a problem with using a metal adaptable box to terminate SWA into something that isn't designed to take SWA. I did an EICR on a property the other day where it had a plastic CU that someone had taken a 10mm SWA garage feed off, they did exactly that, a 4" metal box under the CU, glanded the SWA into the box and passed the inner cores straight through into the MCB, everything properly earthed though.

They could have terminated the SWA straight into the plastic CU but would probably have snapped it off terminating the wires, I've seen loads damaged in this way over the years, or they could replace the whole board for a metal one at great expense but if it was done before metal boards were available, what then. Customer has a choice between a £500 new consumer unit or a £4.99 metal box, what would you choose.
 
Dont see a problem with using a metal adaptable box to terminate SWA into something that isn't designed to take SWA. I did an EICR on a property the other day where it had a plastic CU that someone had taken a 10mm SWA garage feed off, they did exactly that, a 4" metal box under the CU, glanded the SWA into the box and passed the inner cores straight through into the MCB, everything properly earthed though.

They could have terminated the SWA straight into the plastic CU but would probably have snapped it off terminating the wires, I've seen loads damaged in this way over the years,
Why should anything snap is it's done properly?
or they could replace the whole board for a metal one at great expense but if it was done before metal boards were available,
Metal boards have always been available
what then. Customer has a choice between a £500 new consumer unit or a £4.99 metal box, what would you choose.
good workmanship
 