I would be interested to know which of my posts make you think i don't understand the term "extraneous" conductive part, at least i can spell it ;) :D

By the way in the OSG section 4.7 page 31 it says "supplementary bonding is not required to metallic pipes supplied by plastic pipes"

apologies as well if i have been a bit off with anyone!


Apologies, I seem to have merged your post with someone else's in my head, after re-reading, I can see nothing to back up my previous post:D
I'm fully aware of what the OSG says.

FYI, it was a faulty keyboard, rather than operator error:eek::D

I see what you are saying here....but you cant stop at just plastic sections,compression joints are electrically unreliable,are you going to do a continuity test on every single pipe in the building between each electrically suspect joint and perhaps link across compression joints?
A sledgehammer to crack a nut IMHO....just stick to the requirements of BS7671.
I understand your point entirely. There was a similar thread about this a few weeks ago, someone wanting to know if they needed to bond radiators, and short sections of pipe which were supplied by plastic pipe. Whilst I would agree that there is no need to bond individual radiators, I would still expect a metallic heating system to be bonded.

Lets face it, the IEE cant make their mind up about earthing, so I doubt we are all going to agree with each other
wink.gif
smile.gif


This is rather off-topic, I'd be happy to leave it where it is.
 
Last edited by a moderator:
In domestic situations,the minimum cable size to an external building attached to a TNC-s system would be 10mm ( the earth size must be equal to the main protective bonding conductor)
The other way of doing this if your cable to an outbuilding is under sized would be to segregate from the building cpc and install and RCD/RCBO to protect it .
 
In domestic situations,the minimum cable size to an external building attached to a TNC-s system would be 10mm ( the earth size must be equal to the main protective bonding conductor)
The other way of doing this if your cable to an outbuilding is under sized would be to segregate from the building cpc and install and RCD/RCBO to protect it .

Unless there are no bonding requirements in the outbuilding - then a normal size CPC will do (i.e. 6mm SWA...2.5mm cpc):)
 
In domestic situations,the minimum cable size to an external building attached to a TNC-s system would be 10mm ( the earth size must be equal to the main protective bonding conductor)
The other way of doing this if your cable to an outbuilding is under sized would be to segregate from the building cpc and install and RCD/RCBO to protect it .

Can you please give the reg which states this requirement as I dont believe it is right.....happy to be corrected though.
 
Closest I can find is 544.1.1 Where an installation has more than one supply source to which PME conditions apply, a main protective bonding conductor shall be selected according to the largest neutral conductor of the supply.


Cant find anything else hopefully someone else will


Chris
 
Wayne is right....if there is no gas, water or structural steel to bond.

Table 4.1 will give you main protective bonding conductor sizes if there are

Some authorities differ with regards to taking the pme system out to external buildings (ie southern & central networks, eastern don't )

In domestic new build situations providing calculations and networks supplier is ok you wil normally cover every base installing a cable with 10mm cpc. (obviously depending on neutral conductor size)

Forums are a minefield!!!!! contact the NICEIC helpline !
 
I'm still confused as to whether you are stating the minimum size of the bonding conductor to the outbuilding or the size of the cpc.
The size of the main bonding conductor is related to the size of the neutral and earthing conductor at the origin of the installation, and has no relation to the size of the condutors feeding an outbuilding which is either a distribution circuit or a final circuit.
 
Further to my post above I am certain crackedwolf is not correct.
The main bonding to extraneous conductive parts in an outbuilding must be continuous back to the MET at the origin of the installation where TNCS conditions apply. Accordingly it must be sized as required by bs7671 in relation to the neutral and earthing conductor at the origin of the supply.
The supply to the outbuilding itself is either a distribution circiut or final circuit and can be sized in the normal way with reference to load and protective device rating.
If crackedwolf was correct then all circuits on a TNCS system where main bonding is required would have to be a minimum of 10mm.
 
Indeed, main bonding in out buildings, if TNCS supply, should be 10mm min.

One of the reasons for using a rod and divorcing the earth, is to do away with the need to run a separate bond from the "shed" back to the MET in the house.
 
Indeed, main bonding in out buildings, if TNCS supply, should be 10mm min.

One of the reasons for using a rod and divorcing the earth, is to do away with the need to run a separate bond from the "shed" back to the MET in the house.

Yes but as far as I can see crackedwolf has stated that the cable size (as well as the main bond) would need to be 10mm......that is not correct.
 
So can anyone clarify, when specifying a distribution circuit from the main consumer unit in a house to an outbuilding with its own circuits.
If the main house supply is TN-C-S do you need 2core SWA using the sheath as earth or 3core SWA?
Confused!
 
So can anyone clarify, when specifying a distribution circuit from the main consumer unit in a house to an outbuilding with its own circuits.
If the main house supply is TN-C-S do you need 2core SWA using the sheath as earth or 3core SWA?
Confused!

If there are no extraneous conductive parts in the outbuilding, then you will be able to use either as your CPC for the outbuilding.

If there are extraneous conductive parts in the outbuilding, then you will require a 'protective bonding conductor' to be run to the outbuilding and, in this case, the 'third core' or 'armouring' may not be sufficient.

Hope that's clearer:)
 
If there are no extraneous conductive parts in the outbuilding, then you will be able to use either as your CPC for the outbuilding.

If there are extraneous conductive parts in the outbuilding, then you will require a 'protective bonding conductor' to be run to the outbuilding and, in this case, the 'third core' or 'armouring' may not be sufficient.

Hope that's clearer:)
Thanks Wayne,
Does that mean 2 core + sep CPC single core running alongside or 3 core + sheath?
I had thought that 3 core + sheath would be the best option to provide for future flexibilty /upgrade.
There are no extraneous parts at present, but if eg boiler fed heating was to be installed fed from the main house etc this could become an issue and providing for this now would be a relatively small investment.
Also if I wanted to split this supply in a 900mm trench to serve two outside locations what is the preferred method of T ing the cable at that depth?
Sorry to throw another problem into the pot.
 
I think the best way to describe it would be to give an example as each installation will have different requirements.

Lets say you want to supply a brick shed, 5 metres from the house/CU, with a lighting radial and a socket radial.

If no Extraneous Conductive Parts:

You could sellect a 4mm, two-core, SWA cable and use the armour as your CPC/Earth.

You could sellect a 4mm, three-core, SWA cable and use the third core as your CPC/Earth.

Either of these should be appropriate to feed your outbuilding, protected at the house CU by a 32A MCB.

At the outbuilding you would likely have a 30mA RCD main switch and a 6A and 20A MCB respectively.

If there were Extraneous Conductive Parts in the shed:

This changes things completely.

The installation now requires that the extraneous conductive part/s are bonded to the MET (This can be via an 'Earth Marshalling Terminal' - basically a 'remote' MET - as shown in the diagram in post 15)

The bonding of these 'Extraneous Conductive Parts' follows similar rules to the bonding carried out in the house/main installation, so the armour/third core probably wouldn't do.

You would probably be looking at minimum 10mm bonding conductor, so you either run 10mm SWA 3- Core - or you run a seperate bonding conductor alongside your SWA.

The good news is you just connect this conductor to the Earth Bar (EMT) in your garage CU, and use it as a combined CPC/Bonding.

You then run any final circuit CPCs and bonding conductors from this EMT.

That's about as good as I can explain it.

As I said earlier, each installation is different so you have to decide what is best.

E.G. If the outbuilding was 50 metres from the house, you might decide it's easier to rod it.
It's your decision at the end of the day:)
 
I think the best way to describe it would be to give an example as each installation will have different requirements.

Lets say you want to supply a brick shed, 5 metres from the house/CU, with a lighting radial and a socket radial.

If no Extraneous Conductive Parts:

You could sellect a 4mm, two-core, SWA cable and use the armour as your CPC/Earth.

You could sellect a 4mm, three-core, SWA cable and use the third core as your CPC/Earth.

Either of these should be appropriate to feed your outbuilding, protected at the house CU by a 32A MCB.

At the outbuilding you would likely have a 30mA RCD main switch and a 6A and 20A MCB respectively.

If there were Extraneous Conductive Parts in the shed:

This changes things completely.

The installation now requires that the extraneous conductive part/s are bonded to the MET (This can be via an 'Earth Marshalling Terminal' - basically a 'remote' MET - as shown in the diagram in post 15)

The bonding of these 'Extraneous Conductive Parts' follows similar rules to the bonding carried out in the house/main installation, so the armour/third core probably wouldn't do.

You would probably be looking at minimum 10mm bonding conductor, so you either run 10mm SWA 3- Core - or you run a seperate bonding conductor alongside your SWA.

The good news is you just connect this conductor to the Earth Bar (EMT) in your garage CU, and use it as a combined CPC/Bonding.

You then run any final circuit CPCs and bonding conductors from this EMT.

That's about as good as I can explain it.

As I said earlier, each installation is different so you have to decide what is best.

E.G. If the outbuilding was 50 metres from the house, you might decide it's easier to rod it.
It's your decision at the end of the day:)

Thanks Wayne,
Great response, its getting clearer all the time.
Couple of further queries
The water supply to my outbuilding is 32mm Polyethylene Blue pipe fed directly from a street main with my house tee'd off it also in polyethene.
The only metal connections to this pipe in the outbuilding is a tap screwed to a plastic sink and a toilet cistern.
The drainage is similarly plastic connected to the street sewer.
Does the fact that, although the supply pipe is clearly non conductive, water flows in it make it in anyway an extraneous conductive part?
There are no metal gas/oil or water supply pipes coming into the outbuilding ,only plastic.
Also does the diagram at Post 15 hold good for both TNS and TNCS sytems?
Thanks for your help
Graham
 
Got a question on this, looked at a job today, needs a shed at top of garden on supply, was going to run 3 core SWA up to it via the garden wall however the problem is i cant get the supply back to the CU, its a terraces house and the board rite at the front, i would have to rip the house in half to get a cable to it, there is just no way to get there with out them moving out.

the best option is off the utility room ring main as thats where the back door is, the main CU is split load twin RCD


whats the best way of doing this as its really classed as a spur ?

i was going to put a new CU in the shed with 6 and 16A MCB for lights and sockets with a another one in the utility room with the 20A, however the regs state that a fused spur must be limited to a rating of 13A

i was also not going to fit a RCD as per the RCD in series i keep reading about
 
feeding off main house C.U would also be dependent on size of the submain to outbuilding too right? say if using a 16mm 3 core swa would be hard to terminate the earth and neutral in the C.U s so best option would be to split tails into fused switch, earth the swa banjo into an MET and then at outbuilding C.U bring in the 16 mm swa tails and earth with a rod and 10mm? earth
 
Got a question on this, looked at a job today, needs a shed at top of garden on supply, was going to run 3 core SWA up to it via the garden wall however the problem is i cant get the supply back to the CU, its a terraces house and the board rite at the front, i would have to rip the house in half to get a cable to it, there is just no way to get there with out them moving out.

the best option is off the utility room ring main as thats where the back door is, the main CU is split load twin RCD


whats the best way of doing this as its really classed as a spur ?

i was going to put a new CU in the shed with 6 and 16A MCB for lights and sockets with a another one in the utility room with the 20A, however the regs state that a fused spur must be limited to a rating of 13A

i was also not going to fit a RCD as per the RCD in series i keep reading about

How much load is going to be used in the shed?....I would of thought a 13a FCU would cover most sheds.
 

Reply to Supply to OUTBUILDINGS in the Australia area at ElectriciansForums.net