Measured at the input to our house.
Done with a digital scope and downloaded to an excel spreadsheet so I can do the number crunching.
It's the kind of thing I do for power quality analysis but this was just a bit of fun.

A couple of points are immediately evident if you are used to looking at these things.
The flattened peaks are indicative of harmonics, particularly third in this case. Typical on supplies in residential areas - all those electronic gizmos.

The other is the RMS voltage.
251V

[TABLE="width: 142"]
[TR]
[TD]V(av)[/TD]
[TD="align: right"]0.00[/TD]
[/TR]
[TR]
[TD]V(rms)[/TD]
[TD="align: right"]251.25[/TD]
[/TR]
[TR]
[TD][/TD]
[TD="align: right"][/TD]
[/TR]
[/TABLE]
 
  • Like
Reactions: 2 people
It would be interesting to see the effects of harmonics in the area I live, slap bang in the middle of student land. Many are Chinese or Japanese, PC’s, games consoles, you name it they’ll have it.
 
It would be interesting to see the effects of harmonics in the area I live, slap bang in the middle of student land. Many are Chinese or Japanese, PC’s, games consoles, you name it they’ll have it.

I've come across harmonics issues for quite some years now. My field is variable speed drives which are known generators of harmonics. Some these are in the MW range and upwards so harmonics are significant and predictable. Often these have to calculated, presented, and guaranteed at the bid stage - before any contract is placed. Rock and a hard place.

It is par for the course for us to have to include before and after compliance studies.
On one pumping station, in a mainly residential area, the before measurements were non-compliant before we commissioned the variable speed drives. And no worse afterwards.

Initially, that puzzled me. We'd put in some fairly big drives - total installed capacity was about 1 MVA. There was a local dedicated transformer for the sub - (11kV to nominally 400V) so the PCC was at 11kV. The harmonics were measured on the 11kV side.

The explanation isn't altogether complicated. Our drives were a mixture of six and 12-pulse units fed from the three-phase supply.These should result in harmonics no lower than 5th (250Hz).
The the analysis showed a high 3rd (150Hz) content. Single phase non-linear loads.

None very big. Just huge numbers of them and that swamped the contribution from our drives.
And that's what you see on my flat topped wavevorm.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
KVA to amps help
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
geordie,
Last reply from
Besoeker,
Replies
24
Views
3,769

Advert