Currently reading:
Am I being taken for a ride?
Discuss Am I being taken for a ride? in the UK Electrical Forum area at ElectriciansForums.net
I had an electrician come to do a safety check at my property that I let out last week and he has recommended that remedial work should be done at a cost of 2,100 pounds, These are:-
Upgrade of eco 7db
Upgrade of 2 x circuits to RCD protection
Install of isolation point for underfloor heating
identification of points where required
Fusing of points
Enclosure of exposed wiring - these are wires that are not in trunking
Investigation of supply wiring and condition of main isolator and repair
Retermination of required points
cable enclosures
Nothing listed but the sub total is 1,750 plus VAT comes to 2,100
Is that a lot! I last had a test done five years ago, true the wire of the economy 7 is in a situation which is not assessable, however he wants to run a wire from it across the lounge and into the kitchen!
But the amount seems excessive and it is through the Agents who manage the property for me.
Any suggestions would be very helpful.
Many thanks Surreygirl
411.5.2 indicates a TT system and if this is the case I would think a C3 inappropriate.
421.4.9 is not a Regulation at all unless my eyes deceive me.
543.2 has nothing to do with rcds.
421.1.3 has little do do with damaged accessories.
612.3.2 makes no reference to characteristics of the supply.
Good job mate :)
Let those who wish to quote regs read the good book first !
To find one of us who may be near you, take a look here:-
Find an Electrician, Plumber or Tiler | Electricians Forum - Talk electrics and electricals with fellow professional electricians - http://www.electriciansforums.co.uk/categories/find-an-electrician-plumber-or-tiler.84/
You then have two options... you can go to the directory section and search I believe or you could post in the Looking for a domestic electrician section with a rough idea of the job.
You might be advised if you use the directory, to check they have recently been active... then at least if they make a hash of it you can come back tell us all about it and we can proceed to ridicule them into doing the job properly :)
Good luck.
Don't get electricians through estate agents either. They probably get a kick back.....
Partly disagree there Murdoch. I know several estate agents whom I get work from, no kickbacks whatsoever. I also know other trades that also do work through estate agents with the same outcome. I know this because one is a gas lad and the other a painter and I am pretty pally with them.
Obviously it does go on though.
Absence of RCD (411.5.2; 531.2 C3
Absence of RCD 421.4.9; 543.2 C3
Accessory damaged 421.1.3 c2
Inconsistent resistance values for ring circuits F1
Characteristic of supply do not conform to industry standards 612.3.2 F1
Insulated cable not taken inside the enclosure of an assessor 412 C2
This what he has said in the report for a safety certificate
Whereabouts in Surrey are you?
Hampton Wick near Kingston upon Thames
C3 is improvement recommended only, so technically you are not required to have anything done for these items to achieve a satisfactory report. What I find interesting is the regulations stated there... 411.5.2 relates to TT earthing systems (what does the report claim your earthing system is?), 531.2 relates to selection of equipment and outlines some key characteristics of the RCDs we are supposed to use, 421.4.9 does not exist in the regs (this may be a typo) and 543.2 details the different types of protective conductor and what is allowable in terms of their implementation and is nothing to do with RCDs.
Accessory damaged C2, this is a legitimate item that requires work providing the item is actually damaged.
Inconsistent resistance values for ring final circuits, Further Investigation. Whether this requires further attention depends largely on what this statement means. If the values are varying by say 0.01 ohms between tests, this could simply be due to the tolerances of the test equipment in use, certainly I wouldn't be worried about it. But if say, r1 is radically different from rn or r2 is way off roughly 1.667 x r1 (or rn), then there could be a bad connection which needs to be investigated to ensure the ring is safe for continued operation. Has he supplied the values of r1, rn and r2 for the RFCs in question?
Characteristic of supply do not conform to industry standard 612.3.2... interesting... 612.3.2 in the regs relates to what constitutes acceptable values for insulation resistance test results and has nothing to do with the characteristics of the supply (which include things like 230v nominal voltage, 50Hz nominal frequency and other important values). So I have absolutely zero clue what he's getting at with this other than possibly just BS to justify charging you an indeterminate fee for investigating a problem which may not actually exist.
The insulation not taken inside an enclosure, yes, that can be a problem but it depends on where it is and what it is as to whether you can legitimately do anything about it. If it's in the meter cupboard for example, you're not responsible for much of what's in there and fixing some of it may require the presence of the seal fairy to cut the seals off the meter/service head (we're not supposed to do that).
You want it to be safe, but with the limited information available, I'd say this guy is a chancer trying to take you for a ride.
Definitely, find a spark from the forums who is local to you and take the advice the guys have given you... get a second opinion from someone else. This could be either a brand new EICR (don't got for a cheap one, on your average house, I look to be there all day and would charge around £240) or engage someone to work through the report and double check what the original guy has put down (as I said, I've done that for someone for a house sale and it cost them around £120 plus materials - in that case, the guy made some very dodgy claims about work that supposedly needed doing and the suggested remedy included a new consumer unit which would have resulted in a bill significantly higher). And of course, please come back and let us know how it turns out.
Sorry to keep asking, The electrician is coming tomorrow with the Agent. Can ou give me some questions to ask him.
Another thing is the main electrical; supply box to the economy 7 is in the lounge. Yes he wants to run an electrical cable through the lounge to the main electrical box in the kitchen. Why does he want to do this it has its own mains box in the lounge! Helllllllp!
So first question... is this the electrician who carried out the report and who wants to do a load of work? I'm assuming it is. Why is the agent involved?
We're going to need to see some pictures to advise further really because doing this from afar, blind, is very difficult. Also, is there anything else on the report... if it's paper, print it, take photos and redact identifying details, then post them. An EICR which is what you should have has various sections on it, and it's important we see them all if we are to try and help you further.
I can think of no reason why he would want to link the main consumer unit/fuse box to the economy 7 one... I've actually got a quote to do where some numpty has done this and now the storage heater in my clients bedroom is on permanently.
If you or the Agent have not received an EICR certificate, ask for a copy, as for the question of running a cable from the E7, I'm unsure, it could be he is attempting to link the E7 box to the Consumers unit (CU) in the Kitchen.
It's very difficult to imagine what he means from your description, not your fault, (you are inexperienced in the realms of electrics,) Having never met the Electrician, we can't really draw an accurate picture of his abilities, he will I think try to get the Agent on his side and baffle him with the same ideas as he has tried to hoodwink you. I think your first priority will be to get your hands on the EICR,
http://www.electricalsafetyfirst.org.uk/mediafile/100404922/Best-Practice-Guide-4-Issue-4.pdf
I have included the best practice guide for you to look at, if the "sparky" attempts to give a typed report which has no resemblance to the certificate in the guide, well then your suspicions will be proven to be true, good luck and please keep the forum posted.
yep. nothing on today, going to have a bit of a tidy up in garage. tomorrow, got a park homes street lighting conversion to LEDs.(weather permitting).
Sorry OP here is a typical EICR cert
http://www.electricaltestcertificat.../Electrical-Installation-Condition-Report.pdf
It now turns out that he wants to check the main supply to the flats! I am sure this is fishing for more work. Thank you for that. Why does he want to check the main supply to all the flats!
I cant see a cert in the pdf mate... What page is it on?
Hi Spoon just posted a EICR PDF
a full EICR is 8/9 pages. should contain a schedule of circuits with all the test readings.
Just posted one Tel not sure if it's current, but suitable for the OP's purposes I think
Who knows it is probably something he should have checked whilst doing the EICR.
Reply to Am I being taken for a ride? in the UK Electrical Forum area at ElectriciansForums.net
