have been told i could have had my parents and brother in prison and killed people and i am starting to wonder if i should find another job tbh.

I doubt that information came form a reliable Legally qualified source, It was from the electrician I suspect.

As second fix and powering up took place after the wall was plastered and the nail had been put through the cable and only hours before the incident, the fault should have been found by the Electrician in his final testing.

The purpose of testing at second fix is to check there has been no damage to cables.
It doesn't matter who put the nail in the cable or if it was cut by a plasterers trowel or nailed though the skirting by a Joiner, The Electrician should have found it.

If the nail was put in after second fix, that would be a different matter.
 
So what he is saying that your dad and brother are liable because he is putting the blame fully on you and taking no responsibility himself... it was plastered a month ago... irrelevant... if tbe install was done correctly and you could get a shock from the wall then it should of shown up in testing... he hasn't done the testing properly and is bricking it because he probably got a low IR result and just thought -------s to it I'll put it's ok and get a job out of it at a later date... this guy sounds like hard work and is very quick to pass the book and from what he said he doesn't really know what he's talking about with regards to anyrhing but is probably just panicking because he wants his name clear

I know some people think that it may not flag up but I'm convinced that if I'd of done that test then I would of seen a strange result
 
thanks spinlondon, so the rcd not operating is whats not making sense to me.

RCDs are there to prevent serious injury or death.
They don't stop electric shocks.
It's very unlikely the person involved would have died, the RCD would have tripped had the fault current have been high enough.
 
There's a lot of possibilities here that a lot of what has been posted is pure speculation. Such as the IR testing may have been done before second fixing took place.

As I, and others have posted, IR testing may well not identify this sort of scenario and the RCD may well hold as there was probably very little current running through the installation when energised.

We need to know if the RCD did indeed operate as designed when human contact was made with the fault.

Luckily no one was seriously injured. An investigation may well happen but with things like this there is no single cause, just a sequence of events that link up. You were one link in this chain of events, there are other links so the finger will not point solely at you.

For now, learn from it and move on. Stop sticking nails in bits of copper!!!
 
he said they would get a 6amp shock and it could kill them because it was over so many milliamps and because it was a floating earth rcb wouldn't operate. i'm starting to get ----ed off with this guy now
 
he said they would get a 6amp shock and it could kill them because it was over so many milliamps and because it was a floating earth rcb wouldn't operate. i'm starting to get ****ed off with this guy now
Think you need to employ an electrician who understands how electricity works. This one clearly doesn't.
 
The only thing that is correct is that it takes like 0.5A to kill someone might even be less but it's like that figure... very low... needless to say we have rule someone out of this.... why on earth (get it hahahaha) did the customer touch the wall!!! It's their fault!!! They shouldn't just got around stroking walls
 
Fair enough the thread has explained the need for testing and how that testing may or may not have been evident,however,we have wiring regulations that are constructed so that the general public (who may be assumed to have no understanding of how electrics behave)are protected by the set standards of installation work and the testing regime that follows and also by protective devices,which should, as fully as possible, protect the person from serious injury should a occurrence take place

If all these were in situ,this builder, who made a mistake,he bears no responsibility whatsoever for the shock sustained by the customer

He is not trained in this trade,he is not expected to know that he could cause danger by his actions
It is for standards and us alone to shoulder any responsibility for lack of safety, whether through poor or inadequate testing,or poor installation standards,the general public and other trades are not to be the fall guys
 
my nail was making the capping live i am told and there was no imbalance between neutral and live because it was going back to the substation.,,....

This is the main reason I never use metal capping. IMO if used it should be earthed, and it never is. It's pointless because it will not provide any more protection to a cable than plastic which carries far less risk.
 
The RCD should of tripped though as there would be an imbalance between line an neutral...As westward10 says there is no guarantee an IR test would pick it up although you would of thought the metal back box that's earthed and in contact with the damp plaster would pretty much guarantee an unacceptable IR reading. Something isn't right IMO.
Agree the IR must've been less than expected, so probably not done prior to making live (or ignored as already mentioned). If RCD didn't trip then I'm guessing the good folks may've been getting less than 15mA when they completed the circuit ... the pain just goes on and on.
 
Last edited by a moderator:
This is the main reason I never use metal capping. IMO if used it should be earthed, and it never is. It's pointless because it will not provide any more protection to a cable than plastic which carries far less risk.
Too difficult to Earth correctly to the regulations as it would be inaccessible is probably why it never is earthed.
 
  • Like
Reactions: DPG
He couldn't have been up to much if the capping just fell off the wall. Sounds as though he didn't do the required testing to me as well.
the capping must have been nailed by more than one fixing.
Too difficult to Earth correctly to the regulations as it would be inaccessible is probably why it never is earthed.
I always try to have it touching metal k.o. box as much as I practically can.
 
i am starting to wonder if i should find another job tbh
I can understand you may feel very disheartened about this whole incident. I would say just stick to your job and don't stray outside what your skills are.
I am worried about your incident with the mains cable and you feeling out of sorts and the symptoms you describe. Did you go to hospital and get checked out? You may have done some damage to yourself internally and should get a check up!
If I were the electrician I would feel responsible for the incident as to whether that is really legally so I do not know. I certainly would have been as co-operative as possible in such a serious situation and shared any tests and tried to get to the bottom of why the RCD did not trip. I guess (?) there must have been a socket on the wall or switch within the area of the wall that was carrying voltage/current which if earthed should have made the trip go. I find the whole story is one which makes me worried about my own work and wanting to make triple sure I have done all tests correctly and that the results make sense and comply with regs etc. It is a cautionary tale for all of us. Finally take heart and don't let this get you down, as there is no real harm resulted from this incident fortunately, it could have been a lot worse. Just use the experience to inform your future methods.
 
a lot has been said about the fact that testing should have found the fault. recently i'd just tested a socket ring. continuity and IR @ 500V. all IR readings >299 Meg. on energising with no loads on the circuit, the MCB tripped. second IR test @1000V gave >599Meg (different tester). fault was nicked insulation on L conductor arcing t back box. so much for testing.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Have a major problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
102

Advert

Thread statistics

Created
james stas,
Last reply from
Sparkingmad,
Replies
102
Views
10,720

Advert