I'm building a flat-roof extension on my house and I've got a guy helping me. Sadly he's miss-drilled the holes in the joists right next to the wall (within 70 mm) instead of .25 - .4 of the beam length. Actually, it looks very nice, but not in line with BRs. If we move the wiring (and pipes actually) to be in line with BR, how should I patch the holes? Can I put a steel plate over them? What to do.

Steve.
 
I'm building a flat-roof extension on my house and I've got a guy helping me. Sadly he's miss-drilled the holes in the joists right next to the wall (within 70 mm) instead of .25 - .4 of the beam length. Actually, it looks very nice, but not in line with BRs. If we move the wiring (and pipes actually) to be in line with BR, how should I patch the holes? Can I put a steel plate over them? What to do.

Steve.
Probably need the advice from Building control
 
  • Like
Reactions: SteveBz
Personally I would get a length of wood the same dimensions as the joist, running from the end of the joist to maybe a couple of feet past the last incorrectly drilled hole and then glue and screw it to the original.

But, as @Pete999 says, getting the advice of building control is probably the best option.
 
Hi - I like steel too, this might do it :) . Wickes Galvanised Jointing Flat Plate 63x300mm | Wickes.co.uk - https://www.wickes.co.uk/Wickes-Galvanised-Jointing-Flat-Plate-63x300mm/p/152829

IMG_1132.jpg
 
  • Like
Reactions: ruston and SteveBz
Hi Guys, Thanks for this. It looks like a steel plate then, but check with building control.

Steve
 
I'd just cut some 12mm ply or OSB, the same height as the joists, spanning the holes a good distance and screw a piece on both sides. Don't forget, some joists are just an OSB web these days anyway, so it's certainly strong enough...

wood-i-joists.jpg


This is not a load bearing joist, it's just a flat roof. If the joists have already been over-sized/specced due to some insulation requirement, then see if BC will just let you leave it as is.
 
I'd just cut some 12mm ply or OSB, the same height as the joists, spanning the holes a good distance and screw a piece on both sides. Don't forget, some joists are just an OSB web these days anyway, so it's certainly strong enough...

wood-i-joists.jpg


This is not a load bearing joist, it's just a flat roof. If the joists have already been over-sized/specced due to some insulation requirement, then see if BC will just let you leave it as is.
Great answer. And I think they have been over-sized because of insulation. They're 150x50 with 100mm insulation.
 
When the water clowns did this on one of our jobs the fix was to put short sections of joist timber on both sides of the joist covering the holes and coach bolted through.
This looked like overkill and may well have been the NHBC inspector making a point or just satisfying his own little power trip
 
Glueing and screwing a sister-plate will be fine, provided the correct glue is used. Something like WEST system epoxy, not Gripfill.The screws are really only needed to clamp up the sister until the glue sets. Most glued joints are stronger than the wood itself, and structurally there is no reason why you couldn't use this to beef-up a joist prior to drilling it to take pipes and cables in an area normally prohibited. Unfortunately, BC are not very inventive...
 
  • Like
Reactions: DPG
If the roof is not load bearing apart from the flat roof or tiles then i wouldnt worry too much brace it as others have said with additional timber or steel brackets/plates.
 
I think they have been over-sized

Check your span and centre to centre spacing against this table...
(taken from "Building Control Guidance Note, Subject: CEILINGS AND FLAT ROOFS, Timber sizes and construction details")

flatroofjoistspans.jpg


...to check if they actually are oversized first. (i'm guessing not, now, unfortunately for you.)
 
Knock up some wood dowels and hammer into holes with some PU wood adhesive let dry and trim off ends, then as sparky chick said glue and screw 18mm ply either side of the joist 500-600mm past the holes if possible,should be more than adequate for a flat roof
 
Check your span and centre to centre spacing against this table...
(taken from "Building Control Guidance Note, Subject: CEILINGS AND FLAT ROOFS, Timber sizes and construction details")

View attachment 43411

...to check if they actually are oversized first. (i'm guessing not, now, unfortunately for you.)
You're right, I've just checked. It's on the edge.

But I'm happy with the solutions suggested here.
 
  • Like
Reactions: rsgaz
what size holes? if only 20mm or 25mm, i'd not bother doing anything. it' s not as if the joists were load bearing.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fixing a miss-drilled beam
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
61

Advert

Thread statistics

Created
SteveBz,
Last reply from
Intoelectrics,
Replies
61
Views
12,292

Advert