Hi all, I've just taken my AM2 and figured I'd post some information and advice.
First up, if you get offered a Pre-AM2 session by your training provider... take it. Go along, make copious notes and pay attention. I learned an awful lot about it.
Composite installation (8.5 hours)
You have to install 7 circuits as follows:-
And the final part (which may fill you with dread) is the heating system.
You get clear wiring diagrams that tell you exactly what protective devices to use for each circuit and which phase they are connected to. The diagram also tells you exactly what type and size of cables to use.
My tips...
Fault Finding (2 hours)
You have to find 7 faults. You have to work through them in order and you have to have an attempt at each before moving on.
My tips...
For each one, you have to provide a brief description of the fault, the location and the fix. Here's an example for a fault on the ring circuit...
I had a data cabling misconnection, a high resistance connection on a bonding cable, a couple of neutral earth faults (shorts), a phase earth fault (short), a broken cable and another I can't remember
Again, being logical and methodical about it, you should be able to complete this quickly. If you don't have a lot of experience with fault finding, try and get some before the event. The trickiest thing I guess if you're not that experienced is finding faults on ring finals. If you've got say a neutral/earth fault, how do you find it... well, you pick a point which is roughly central on the ring (in this instance it's easy as it's socket - sfcu - socket, but in reality it can be a guessing game) and then you split the ring (disconnect the conductors at fault at that point) and test each half. You should find the fault is on one half, so you split that half in half and test each half and so on until you find leg of cable with the fault on it. For things like breaks or high resistance joints on rings there are other approaches that can yield a result faster, but if in doubt (certainly for IR and breaks) splitting the ring will yield results quite quickly.
The gear I used during my fault finding session... insulation resistance tester, continuity tester on the MFT, AVI with continuity indicator and a data cable tester.
Risk Assessment and Short Safe Isolation of Board (45 mins)
The risk assessment part... don't go mental on this. The instructions are clear, risk assess the assessment centre. So as an example... you don't need to talk about respiratory protection as you're not going to be cutting board or drilling holes. On the day I did mine though, it was raining heavily and the floor is painted... slip hazard from a wet floor that could affect anyone entering the building, can be mitigated by putting a suitable mat down
Safe isolation of the board... standard procedure... but for gods sake don't forget to ask the client if you can turn the power off (I did, but remembered and pointed out my mistake).
First up, if you get offered a Pre-AM2 session by your training provider... take it. Go along, make copious notes and pay attention. I learned an awful lot about it.
Composite installation (8.5 hours)
You have to install 7 circuits as follows:-
- Carbon monoxide detector - FP200 cable from DB to FCU in dado, then glanded out onto cable tray (bolted P clip fixing), glanded into detector mount
- Lighting - T+E from DB to first 2 way switch, 3+E to intermediate switch, 3+E to last switch (all in dado), T+E in trunking up to light. Note - The supply goes to the first switch, then the 3+E carries two switched lines, the neutral and CPC until the final switch
- Ring circuit - Singles from DB to 1st socket, then to SFCU, then to last socket and back to DB and singles from SFCU to spur socket (all in dado/conduit)
- TP+N 16A Socket - XLPE SWA from DB to isolator (fixed to tray with tie wraps), singles from isolator to socket
- Motor circuit - Singles in metal trunking to DOL starter then SY to motor, tie wrapped to tray
- Heating - Singles in metal trunking to SFCU
- Cat 5 data connection - Cat 5 cable from one outlet to another, all in dado
And the final part (which may fill you with dread) is the heating system.
You get clear wiring diagrams that tell you exactly what protective devices to use for each circuit and which phase they are connected to. The diagram also tells you exactly what type and size of cables to use.
My tips...
- Read the diagram and the information thoroughly before you start. Some cable sizing info is on other documents, but it is all there
- Follow the steps as laid out in your candidate manual with one exception... do the heating last as most of it is simply following the wiring diagram and connecting it up to the wiring centre (which is a big set of DIN rail mounted Wago spring clamp terminals) That's not to say there isn't wiring to do, but it's a total of 13 cores in singles (from solar controller to circulator - 3 cores LNE, from wiring centre to room stat - LNE Lreturn, from wiring centre to programmer - LNE Lr1, L2, Lr2)
- There isn't too much thinking ahead needed, but do look at the tray that the bonding will be mounted on... there will be two sets of cables on that tray... the SY and the bonding... you don't want them to cross
- When running the ring, check the cable sizes for the heating circuit... mine were the same size so I ran the feed to the heating SFCU in at the same time
- When running the singles in... get all the cores you need together (if you need to use multiple cores of the same colour - like in some of the heating connections, mark them with insulating tape on the start of the core and the reel). Tape them together and run them in. You should be able to run them all in without using a fishtape except for the run from the programmer to the heating wiring centre
- When running in the ring... tape the cores of legs together at each termination point, especially at the DB
- Don't forget to sleeve conductors
- If you do forget something, make a note of it and go back to it
- If you've never worked with FP200, don't worry too much, it's not too bad. Doesn't bend easily and the sheath is quite tough. To strip it, run a knife round the sheath and then bend at the cut and the sheath should begin to split
- If you've never worked with SY cable, go to a local supplier and pick up a couple of metres and a set of CXT glands and practice (you peel the braid back, split it and wrap it into two tails one on either side of the central core - these go into slots on the gland to be sandwiched and secure by two large flat washers, wrap them around and cut them off when they reach the other slot, don't let the braid tails stick out the washers)
- Be careful with the SWA, SY, FP200 and Cat5 cable - You get one shot as you are supplied with precut lengths, so measure carefully
- Don't worry about dressing cables too much... BS7671 does not require the board to be a master piece of cable dressing, chuck it in... if it works properly it doesn't matter if it's messy (I cut one segment of my FP200 a bit short of it looked awful in the DB but wasn't under strain and so was compliant)
- Do worry about excess copper on display
- Don't overtighten things - They undergo a lot of abuse, something I learned early on when I broke a screwdriver blade
- Don't leave the lamp in the luminaire - As above, it's had a lot of abuse and the clips that normally retain them nice and tight are like to be crap (I know this because mine fell off and smashed on the floor)
- Keep your work area tidy - When the cover comes off the board set it to one side, slightly open, take the dado covers off and stack them behind the board cover, take the metal trunking lids off and stack them on top of the trunking. Keep the tools to one side so you don't trip over them
- Don't be afraid to use the AVIs at the centre during the installation phase if you want to check something (identify a cable for example if you didn't mark it with tape), confirm this with the assessor obviously, but they are there for you to use
Fault Finding (2 hours)
You have to find 7 faults. You have to work through them in order and you have to have an attempt at each before moving on.
My tips...
- Look at each fault and think about it for a short while and use the definition to pick the right gear
- Remember that there are only certain locations faults can be (because they have to conceal the cabling that creates the faults - i.e. it can only be inside the trunking and any box marked 'Candidates must not open/remove') - So if you get a fault on the 16A socket outlet... the location can only be after the isolator, since the supply is run in SWA from the DB to the isolator
- The types of faults are breaks, misconnections, shorts or high resistance connections
- If insulation readings were difficult to obtain, don't forget to check N-E
For each one, you have to provide a brief description of the fault, the location and the fix. Here's an example for a fault on the ring circuit...
- Fault is a short circuit between neutral and earth
- Location is between SFCU and dado socket
- Fix is run new earth/neutral cables from SFCU to dado socket and retest
I had a data cabling misconnection, a high resistance connection on a bonding cable, a couple of neutral earth faults (shorts), a phase earth fault (short), a broken cable and another I can't remember

Again, being logical and methodical about it, you should be able to complete this quickly. If you don't have a lot of experience with fault finding, try and get some before the event. The trickiest thing I guess if you're not that experienced is finding faults on ring finals. If you've got say a neutral/earth fault, how do you find it... well, you pick a point which is roughly central on the ring (in this instance it's easy as it's socket - sfcu - socket, but in reality it can be a guessing game) and then you split the ring (disconnect the conductors at fault at that point) and test each half. You should find the fault is on one half, so you split that half in half and test each half and so on until you find leg of cable with the fault on it. For things like breaks or high resistance joints on rings there are other approaches that can yield a result faster, but if in doubt (certainly for IR and breaks) splitting the ring will yield results quite quickly.
The gear I used during my fault finding session... insulation resistance tester, continuity tester on the MFT, AVI with continuity indicator and a data cable tester.
Risk Assessment and Short Safe Isolation of Board (45 mins)
The risk assessment part... don't go mental on this. The instructions are clear, risk assess the assessment centre. So as an example... you don't need to talk about respiratory protection as you're not going to be cutting board or drilling holes. On the day I did mine though, it was raining heavily and the floor is painted... slip hazard from a wet floor that could affect anyone entering the building, can be mitigated by putting a suitable mat down
Safe isolation of the board... standard procedure... but for gods sake don't forget to ask the client if you can turn the power off (I did, but remembered and pointed out my mistake).