I have a supply in a log cabin, in the cabin is 6 double sockets and a couple of lights. Cables are in PVC conduit and are 2.5mm singles sockets and 1.5mm lights.

Sockets

L-L = 0.15 ohms
N-N = 0.15 ohms
E-E = 0.18 ohms
L1 with E2 & L2 with E1 = 0.07 ohms

L to E = >1000+ MG Ohms
N to E = >1000+ MG Ohms
L to N = >1000+ MG Ohms

Ze at board is 0.28 ohms 843 Amps.

Tested at socket Uc Rl 20 Amp 60898 type B

Socket 1 1.62 ohms 50V 0.04 V
Socket 2 1.29 ohms 50V 0.03 V
Socket 3 1.65 ohms 50V 0.05 V
Socket 4 1.62 ohms 50V 0.04 V
Socket 5 1.52 ohms 50V 0.04 V
Socket 6 2.12 ohms 50V 0.04 V Zs value to high.

This socket is approximately 300mm through a wall away from another socket. Only difference is that it is a waterproof socket with a neon indication. I have tried inserting the plug in and out numerous times in case of bad contact. I have taken the reading from the rear of the socket across the terminals and still the same problem. I am trying to come up with a reason for this.

Could change the mcb for 16A, but still can’t find the reason why it should be different than the others.

Any ideas?

Adie
 
take a reading at the outgoing side of the MCB. the difference between the reading you get and the Ze is internal res. of MCB.
 
get cabin to -267 degrees then youl have a super conductor and should disconnect in time
 
Could it be due to tarnished connections on the outside socket ?

Is the outside socket part of the ring, or a spur ?

The other readings in your post look to be correct.
Sockets

L-L = 0.15 ohms
N-N = 0.15 ohms
E-E = 0.18 ohms
L1 with E2 & L2 with E1 = 0.07 ohms

Are you using the no trip setting (live test), or (R1+R2) (dead test) at the S/O's ?
 
As its a socket should be on a RCD anyway, in which case Zs up to 1667ohms.

I had thought about that too, but it should still be investigated for the higher reading, as you should not use the RCD as an 'excuse' for poor readings, I agree though it will mitigate an expected higher reading.
 
  • Like
Reactions: 1 person
could be a spur, rcd , bigger cable, change mcb
 
i tend to disagree with the osg figures. why? because that 0.8 factor assumes that the cable will be loaded enough to run at it's rated operating temp. of 70deg. that situation, in a domestic environment is as rare as rocking horse poo.
 
  • Like
Reactions: 1 person
I have a supply in a log cabin, in the cabin is 6 double sockets and a couple of lights. Cables are in PVC conduit and are 2.5mm singles sockets and 1.5mm lights.

Sockets

L-L = 0.15 ohms
N-N = 0.15 ohms
E-E = 0.18 ohms
L1 with E2 & L2 with E1 = 0.07 ohms

L to E = >1000+ MG Ohms
N to E = >1000+ MG Ohms
L to N = >1000+ MG Ohms

Ze at board is 0.28 ohms 843 Amps.

Tested at socket Uc Rl 20 Amp 60898 type B

Socket 1 1.62 ohms 50V 0.04 V
Socket 2 1.29 ohms 50V 0.03 V
Socket 3 1.65 ohms 50V 0.05 V
Socket 4 1.62 ohms 50V 0.04 V
Socket 5 1.52 ohms 50V 0.04 V
Socket 6 2.12 ohms 50V 0.04 V Zs value to high.

This socket is approximately 300mm through a wall away from another socket. Only difference is that it is a waterproof socket with a neon indication. I have tried inserting the plug in and out numerous times in case of bad contact. I have taken the reading from the rear of the socket across the terminals and still the same problem. I am trying to come up with a reason for this.

Could change the mcb for 16A, but still can’t find the reason why it should be different than the others.

Any ideas?

Adie

Are you getting this reading at each socket or is that just what you get at the connections at the DB??
 
  • Like
Reactions: 1 person
ther is a a sum to work it out as tel said its on the side of safety
 
Sorry tried to edit my last post but it did not appear.

The socket is part of the ring circuit. The cabling is exactly the same on all sockets. It is a TNC-s system, I pushed the plug of the tester in and out numerious times so hopefully no tarnished connections. I also took reading from rear of socket. The DB is a MCG fuseboard with a 2P6330 RCD and 2 x 60898 mcb’s 1x 20Amp 1 x 6Amp. What is the table or reg that says about rcd controlled socket can be 1667 ohms.
 
  • Like
Reactions: 1 person
Am I missing something?

Shouldn't the reading be 0.35 (or even less with parallel paths) at all the sockets?


1666 ensures the RCD will disconnect before voltage rises above 50V.
It should not be used to ignore maximum Zs values - unless unavoidable (e.g. TT)
 
  • Like
Reactions: 2 people
table 41.5, p50 in the red book. not sure where in bgb.
 
pushed the plug of the tester in and out numerious times so hopefully no tarnished connections

I meant where the cables terminate in the back of the SO too, as your end to end readings were ok.

What is the table or reg that says about rcd controlled socket can be 1667 ohms.

Table 41.5 (BGB) p57.

It actually says anything above 200 may be unstable wrt Earth rods.

Edit: Tel beat me to it, again! lol
 
Last edited by a moderator:
  • Like
Reactions: 1 person
the 1667Ω figure is for earth faults, and not for live-n faults. I would carry out a Zp-n, which means that you test between live and neutral, not live and earth. If your using a fluke, its just a case of swapping the leads over, but if its a megger, then youll have to use the probes. If this comes up ok, then youve identified that it is indeed a problem with the earth path, and not the live. If it comes up bad, then it means that you have problems wiuth either your live or neutral.
 
  • Like
Reactions: 1 person

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Socket Zs High
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
89

Advert

Thread statistics

Created
AdieB,
Last reply from
Des 56,
Replies
89
Views
16,680

Advert