Vanman my friend

I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a *a current short circuit(L-N).

As Zs between L-E has a higher value, than Zs between L-N, only Zs for L-E is measured.

CPC wire on a 6mm T&E is 2.5mm, and N wire is 6mm.
Therefore current through the L-CPC path( 6mm+2.5mm) will be less, than the Current through L-N path(6mm+6mm).

If there is no earth continuity then its potentially fatal, but if Neutral is missing or non continuous then it no big deal, it comes apparent in the functional test.

My names not Glenn!

OK, I see where your coming from but having a good Zs does not guarantee that the L-N impedance is lower - there could be a high resistance connection somewhere on thev neutral!
 
Last edited:
My names not Glenn!

OK, I see where your coming from but having a good Zs does not guarantee that the L-N impedance is lower - there could be a high resistance connection somewhere on thev neutral!

Thank god we r on the same page

I agree with your comment of a Hi z on the N wire.

But that's another reason why Zs is measured between L-CPC, it ensures the earth fault durations are limited.
 
But that's another reason why Zs is measured between L-CPC, it ensures the earth fault durations are limited.

But that's what Zs IS ​- earth fault cuurrent

The same test between L & N is called the prospective short circuit current.

The greater of these two is the prospective fault current
 
"I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a 8A current short circuit(L-N)."

Will it?????
ever???
in 0.4s ??
 
Check the cable terminals are nice and tight at both ends going to the suspect socket.

If cable long enough, re-strip and make new terminations.

Now measure Zs at both ends of the cable.

If the cable is only 300mm, replace cable and there should be un-measurable difference in Zs at both ends.
 
Am I missing something?

Shouldn't the reading be 0.35 (or even less with parallel paths) at all the sockets?


1666 ensures the RCD will disconnect before voltage rises above 50V.
It should not be used to ignore maximum Zs values - unless unavoidable (e.g. TT)

Totally agree, should be getting a Zs of around 0.35ohms at each socket outlet. Sounds like a loose connection at one of the sockets.....

Not true!!!

R1+R2 should be the same at each socket outlet. Zs will increase towards the middle of the ring and decrease back towards the DB therefore you will get a reading of around 0.35Ω near the middle of the ring.
 
Not true!!!

R1+R2 should be the same at each socket outlet. Zs will increase towards the middle of the ring and decrease back towards the DB therefore you will get a reading of around 0.35Ω near the middle of the ring.

Agreed to a point (Hence "around" 0.35ohms)
I believe the ring in question is fairly small and the figures the op states seem way off by 1 and a bit ohms....seems alot to me, especially as he states these sockets are all on the ring final and not spurs.
 
"I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a 8A current short circuit(L-N)."

Will it?????
ever???
in 0.4s ??



Geoff, my friend, Zs is the impedance of the circuit, and not a current.

Lister, my friend, a 6A type B CB will trip in 0.4Sec with a minimum of 30A current. 7A & 8A were given as examples.

There fore 230V/30A = 7.67 Ohms is the theoretical max Zs for a 6A type B CB.
 
quote_icon.png
Originally Posted by Moses
Thank god we r on the same page

I agree with your comment of a Hi z on the N wire.

But that's another reason why Zs is measured between L-CPC, it ensures the earth fault durations are limited.



high Z...well that`s changed then....a minure ago it was Zs....


Yes but no, but yes but no, but yes but no Glenn

That Hi Z on the N wire is a fault, faulty connection.!!!!!!!!
 
Agreed to a point (Hence "around" 0.35ohms)
I believe the ring in question is fairly small and the figures the op states seem way off by 1 and a bit ohms....seems alot to me, especially as he states these sockets are all on the ring final and not spurs.


Sipmles he has not zeeored

or

he has a low battery

or

He has a faulty meter
 
I had to send my Megger 1730 back a couple of weeks ago because the EFLI test at a socket (using plug adaptor OR on the terminals) was way higher than I was expecting. As has been said, it can be the internal resistance of the MCB/RCD so that would have to be deducted.
All that said, once I got my new 1730 and did the same tests, they were very close to Ze+(R1+R2), so it was definitely a faulty tester in my case.

Edit... Forgot to add. I have to do a 3-wire no-trip test, as the 2-wire is always at least 0.5 ohms higher!
 
Last edited:
Sorry for delay - something crashed.

Geoff, my friend, Zs is the impedance of the circuit, and not a current.
Yes, I'm sorry. I should have written -

But that's what Zs IS ​- a measured value to determine prospective earth fault cuurrent

The same test between L & N is to determine the prospective short circuit current.

The greater of these two is the prospective fault current.
 

Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on...
Replies
16
Views
3K
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and...
Replies
53
Views
5K
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do...
Replies
30
Views
10K
Hi, I was wondering if you guys can help with some errant test results. I'm testing a ring and i get L-L = 0.41 N-N = 0.40 E-E = 0.63 Great...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock