Vanman my friend
I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a *a current short circuit(L-N).
As Zs between L-E has a higher value, than Zs between L-N, only Zs for L-E is measured.
CPC wire on a 6mm T&E is 2.5mm, and N wire is 6mm.
Therefore current through the L-CPC path( 6mm+2.5mm) will be less, than the Current through L-N path(6mm+6mm).
If there is no earth continuity then its potentially fatal, but if Neutral is missing or non continuous then it no big deal, it comes apparent in the functional test.
My names not Glenn!
OK, I see where your coming from but having a good Zs does not guarantee that the L-N impedance is lower - there could be a high resistance connection somewhere on thev neutral!
My names not Glenn!
Thank god we r on the same page
I agree with your comment of a Hi z on the N wire.
But that's another reason why Zs is measured between L-CPC, it ensures the earth fault durations are limited.
But that's what Zs IS ​- earth fault cuurrent
The same test between L & N is called the prospective short circuit current.
The greater of these two is the prospective fault current
"I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a 8A current short circuit(L-N)."
Will it?????
ever???
in 0.4s ??
Check the cable terminals are nice and tight at both ends going to the suspect socket.
If cable long enough, re-strip and make new terminations.
Now measure Zs at both ends of the cable.
If the cable is only 300mm, replace cable and there should be un-measurable difference in Zs at both ends.
Am I missing something?
Shouldn't the reading be 0.35 (or even less with parallel paths) at all the sockets?
1666 ensures the RCD will disconnect before voltage rises above 50V.
It should not be used to ignore maximum Zs values - unless unavoidable (e.g. TT)
Totally agree, should be getting a Zs of around 0.35ohms at each socket outlet. Sounds like a loose connection at one of the sockets.....
Not true!!!
R1+R2 should be the same at each socket outlet. Zs will increase towards the middle of the ring and decrease back towards the DB therefore you will get a reading of around 0.35Ω near the middle of the ring.
Not true!!!
Agreed to a point (Hence "around" 0.35ohms)
I believe the ring in question is fairly small and the figures the op states seem way off by 1 and a bit ohms....seems alot to me, especially as he states these sockets are all on the ring final and not spurs.
Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
5K
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on...
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and...
5K
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do...
10K
Hi, I was wondering if you guys can help with some errant test results. I'm testing a ring and i get L-L = 0.41 N-N = 0.40 E-E = 0.63 Great...
4K