I am trying to understand the amperage flow in my 200 amp main panel.
In theory, (example only), let's say you had a 200 main panel installed with (7) single pole 20 amp breakers on each hot leg.
So (14) single pole breakers total ...
For the sake of this example let's further assume you had just one outlet wired to each breaker and those outlets all had a hair dryer pulling were plugged in and running (pulling 15 amps each ... If my math is correct, that is 105 amps through each each hot leg. My understanding is that this would NOT trip the main breaker because the panel can only see 105 amps total since each hot leg is out of phase with the other hot leg.
So 105 amps total flow, alternating between the 2 legs (60 times a second) - not 210 amps total.
Do I understand that correctly?
The thing I can't quite get is that you are effectively pulling 210 amps (if all 14 hair dryers are running) yet the panel is only seeing 105 amps.
In theory, (example only), let's say you had a 200 main panel installed with (7) single pole 20 amp breakers on each hot leg.
So (14) single pole breakers total ...
For the sake of this example let's further assume you had just one outlet wired to each breaker and those outlets all had a hair dryer pulling were plugged in and running (pulling 15 amps each ... If my math is correct, that is 105 amps through each each hot leg. My understanding is that this would NOT trip the main breaker because the panel can only see 105 amps total since each hot leg is out of phase with the other hot leg.
So 105 amps total flow, alternating between the 2 legs (60 times a second) - not 210 amps total.
Do I understand that correctly?
The thing I can't quite get is that you are effectively pulling 210 amps (if all 14 hair dryers are running) yet the panel is only seeing 105 amps.