Tidy Max
Hello everyone.
Been to look at a job and found some dado trunking that's fed in singles off a TP isolator. There seems to be 6 2g socket outlets. L1 feeds two sockets, L2 feeds two sockets and L3 feeds two sockets. Then the neutral comes out of the isolator and feeds all 6 (as does the earth).
Will there not be an issue regarding the neutral loading? The tp isolator is fed by a 2.5 5 core SWA then protected by a 20A tpmcb back at the board.
Been to look at a job and found some dado trunking that's fed in singles off a TP isolator. There seems to be 6 2g socket outlets. L1 feeds two sockets, L2 feeds two sockets and L3 feeds two sockets. Then the neutral comes out of the isolator and feeds all 6 (as does the earth).