Dews84

6 amp rcbo moeller was installed in 2009 no work been done in the property since the new consumer unit installed 2009 whoch is a Split load fuse box with unprotected rcd side and protected rcd side. Unprotected side rcbos have been used for the sockets and lights. The 6amp rcbo had tripped and would not reset, the switch was sloppy as t say it was a internal mechanical fault with the rcbo. I therefore piggy backed the line conductors to the rcd side 6amp mcb which controlled the other light circuit which worked perfectly until the next day when I picked up a new rcbo 6amp from the shop. Installed the rcbo as per usual reconnected the line conductors (and the e lead t e bar as previous rcbo didn't have.) all worked fine all lights no tripping etc, so I press the test button on the rcbo and it works but wen I go to reset it won't and a small flash can b seen behind the rcbo on the live busbar. (The other rcbo for the sockets test button works and resets fine) if I switch off the main incoming fuse/breaker then reset the rcbo and then allow the system to come live again by the main fuse all is fine. Any suggestions ?? As I'm pretty stumped with this one. The lights on the rcbo consist of typical ceiling roses and spot lights in the bathroom, the rcbo side of the consumer unit is old colour wiring and the rcd side is new. Please no silly or smarmy answers I have all my papers and I am an electrician
 
Yes I double checked this too as been a common fault with flashing as well as it is a Wylex rcbo not a moeller now, but was told that it was compatable and does fit snug .Any more suggestions?
 
is the C/U a metalclad? Is the line conductor tucked behind the busbar....nicked maybe and shorting onto the busbar...and hence to earth?
 
are you sure ALL connections are tight n secure....line?..neutral?......if all fails at the c/u then test circuit...IR here...
 
The insulation resistance and continuity of the circuit has been done and is satisfactory. The c/u isn't metalclad but the line does go behind the busbar bar but is not touching or 'nicked', and isnt earthing.I also wouldnt ir an rcbo thanks for suggestions tho anymore would be appreciated. All connections are tight.
 
is there a blown lamp anyware on the circuit that this RCBO feeds...perhaps one that you`v missed as youv gon round....could be shorting...
 
SERIOUSLY!!! have you got correct connections cause i know the crabtree rcbos they changed the L and N round.
 
I'll have a look u could be right on this one, but I still don't see why it would allow me to reset it if this was the case Or am I wrong
 
swop the circuit onto another RCBO...if its clear...then its the RCBO thats faulty...if not...start thinking about something on the circuit...
 
Rcbo is new. Previous was faulty.and as I say the circuit worked fine in a normal 6 amp mcb with rcd protection and tested and reset fine. It is only wen I test the rcbo that it will not reset without first switching off the main supply then resetting the rcbo and switching the system bk live then it's fine. But I know this is not the normal operation for rcbo hence y I'm confused I have also taken out he e lead to make sure it wasn't this cause the indifference
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
6 amp rcbo fault
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
Dews84,
Last reply from
Engineer54,
Replies
29
Views
4,899

Advert