B
Bobster
8.5kW will still require a 40A ocpd so the cable design will be the same as the 9.5kW.
No it will not. It's a fixed load application.
Well yeah, there's that too. I'll be honest, it's not an exception to the standard calcs that I use very often.No it will not. It's a fixed load application.
It doesn't matter what ocpd you put as long as the cable has a low enough zs to trip it. If you have 0.01ohm ze and the cable is 3 feet long, you could put an 63a mcb on 1.5mm cable with a bell transformer at the other end.
The issue is the rated current of the shower being suitable for the cable.
Do the calcs with all the correction factors and you will get the answer you need.So will a 8.5 kw go on a 40A with 6mm cable an be within regs as another spark put the fear of god into me by saying DONT PUT A6mm ONA 40A
Good point, didn't think about adiabatic/let through from the low ze. Would need a happy medium. Would anyone calculate the cpc adiabatic for a 6mm shower cable?In that scenario the CPC will be destroyed in an earth fault