Cable size

Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1,228
Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
ah i see!
ecb7171239ea7cb07bb84a69a4c6c3b2.jpg


im usually organized
 
I have got to dig a 2ft deep hole anyway for the mounting plate to be sat in, so can just dig across a little bit and see whats there, unlikely theres anything where this is going though.

What do you think? 2 rods maybe? Its next to a marina too, so the ground might be quite wet (if it leaks)

Famous last words mate. Don't risk it. Especially if 2 rods are required. We install 1 rod at a time then test. No point going further than required.
 
Just a thought if he does TT it, it is close to a metal clad building which is itself TNCS/PME and also likely to be bonded via the structural steelwork , your are not supposed to be able to touch two different earthing systems simultaneously, this can itself be a shock hazard due to the differences between true earth (TT) and the PME earth.

I don't know the reg number off the top of my head, and it may be a DNO rule, I would have to look it up to back this statement up.
 
Yep. If you are planning to work for this customer again I would recommend installing to the 3rd. You don't want some idiot slagging you off in 7 months time saying "he gave you an out of date installation mate". Even though he would be wrong.

He's got more worries than just that if he's installing less than 20mtrs of new SWA with a plastic joint box in the middle of it, not bonding a lump of metal that the charging point is fixed to and connecting it all to a PME supply.
 
Just a thought if he does TT it, it is close to a metal clad building which is itself TNCS/PME and also likely to be bonded via the structural steelwork , your are not supposed to be able to touch two different earthing systems simultaneously, this can itself be a shock hazard due to the differences between true earth (TT) and the PME earth.

I don't know the reg number off the top of my head, and it may be a DNO rule, I would have to look it up to back this statement up.

This was my other part of the jigsaw, its too close, and I know its bonded as have seen it all inside against the back of the skins.

Hmm its not very straight forward is it.

I say just connect to the PME system, its too close.
 
Just a thought if he does TT it, it is close to a metal clad building which is itself TNCS/PME and also likely to be bonded via the structural steelwork , your are not supposed to be able to touch two different earthing systems simultaneously, this can itself be a shock hazard due to the differences between true earth (TT) and the PME earth.

I don't know the reg number off the top of my head, and it may be a DNO rule, I would have to look it up to back this statement up.

it is a minefield eh?

It it is unusual for DNOs to provide earths to metal framed building is it not?

This is job may need a step back and reasses. Many heads are better than one.
 
Im going continuous now actually, you are not up to speed LOL.

It's hard to keep up to be honest, in the last thread about this you had decided to use a three phase unit and now you're back to single phase again. Now you're wandering off into the realms of whether or not it can be connected to PME or not and if it needs earth rods or not.
I thought you would have had this installation designed by now.

Where are you thinking of connecting the earth rods and why? What value of Ra do you need to achieve?

I'd personally be looking to comply with the requirements of (ii) in the list of situations where PME can be used. I can see the sense in divorcing the PME connection and relying on earth rods for one charging point when 99.9% of the time the PME will be fine, and the other .1% of the time the earth rods connected to the MET could benefit the entire installation.
 
Just a thought if he does TT it, it is close to a metal clad building which is itself TNCS/PME and also likely to be bonded via the structural steelwork , your are not supposed to be able to touch two different earthing systems simultaneously, this can itself be a shock hazard due to the differences between true earth (TT) and the PME earth.

I don't know the reg number off the top of my head, and it may be a DNO rule, I would have to look it up to back this statement up.
Should a metal clad building be PME anyhow? I thought not.
 
This was my other part of the jigsaw, its too close, and I know its bonded as have seen it all inside against the back of the skins.

Hmm its not very straight forward is it.

I say just connect to the PME system, its too close.

Absolutly do do not approach it like this mate. If the neutral breaks down on the DNO side and someone goes to use the VC point then their body may well be the return path back to earth.

All together we can get there I am sure.
 
I really do appreciate Kate all your help and constructive feedback on this, it's an area that itself has had the regs fiddled with and also other issues like earth rods and distances to the building.

Ok so if we break it down into small chunks, let's hypothetically say we will go with the earth rod, it says connect it be k to the met. Do we have any information anywhere as to what reading is acceptable that we must achieve?
 
I really do appreciate Kate all your help and constructive feedback on this, it's an area that itself has had the regs fiddled with and also other issues like earth rods and distances to the building.

Ok so if we break it down into small chunks, let's hypothetically say we will go with the earth rod, it says connect it be k to the met. Do we have any information anywhere as to what reading is acceptable that we must achieve?


Kate???
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock