Like above, fitting a VSD 1ph - 3ph would eliminate voltage balance issues, 3ph it is more efficient and reliable and the VSD would be a better option for monitoring the motor however you have not mentioned what KW the motor is, using single to 3ph drives means you effectively load 1 ph up to create 3ph which won't be a issue with a small motor but as the size increases then we have to see if it suitable.
 
I'll look it up, ignore the message if you just saw me post, I forgot you are going to need to run it at 230v 3ph not 400v.

A quick check for a ballpark figure would be 1ph - 3ph VSD and a 3ph 230v motor and the VSD will be about 20amps input needing a 32amp MCB front end device.

Given most submersible pumps are presealed and wired the spec's of the pump would need to match your VSD option and as we are not using 400v 3ph you will need to get a 230v 3ph pump.
 
Last edited:
Woah slow down I am only DIY status ;-)
I have a motor (Grundfos 3VC 2.2kw MS402) which hopefully will be repaired.
My 3 phase supply is unbalanced and changes on a daily basis.
The VSD sounds an interesting solution.
Will it be possible to use that motor with a suitable VSD?
If so can you recommend a respected manufacturer and guide me as to the specs of a suitable device
 
Given your status you will really need to get a pro in as this has to be spec'd correctly and VSD would need setting up, this is not DIY to be fair.
It will be expensive to try do this off this forum as any info you fail to give us could change how it should be done.
It nudges you in the right direction though.
 
Have we considered the possibility that the OP just had a bad pump?
I would think absolutely nothing of slapping a 3-phase motor on a supply that tested as 415-416-422 line voltages.
OP, any chance you were running the motor backwards? Submersible pumps can often still push water running the wrong way, but the flow will be reduced, as will the cooling effect on the motor, these pumps are over-powered for their size and rely on the water flow to properly cool them.
The installer jumping straight to the voltage imbalance smacks of "Yeah, definitely not my motor that failed, must be your supply"
 
You raise a point I missed @Lucien Nunes, why no protective devices tripped here to prevent the failure.
I also wondered about that. Normally speaking the mcb, s will only trip if they can't handle the staring current. The overload will trip if the motor is being overworked. But what about thermistor protection?. They are generally more sensitive to overheating than overloads. Its many years since I worked with motors but I would have thought that overload protection has moved on to the point where issues like the OP, s have being minimised
 
Would not a 3Ph to 3Ph VFD stabilise the voltage and allow the existing pump to be used, Invertek where very helpful when I was looking to slow my swimming pool pump down, may be worth contacting them: Variable Frequency Drive Manufacturer | Variable Speed Drives | AC Drives | Invertek Drives - https://www.invertekdrives.com/
The voltage imbalance that we speculate may have caused the demise of the motor would also play havoc with the VSD giving unwanted voltage DC bus ripple, this could cause unwanted tripping and/or reduce the life of the DC Bus cap's - we can however combat this by fitting DC chokes in combination with AC line reactors but we are ending up over egging the pudding here when we simply can eliminate the whole problem with a 1PH - 3PH VSD.
 
So do you think a VSO is the best way to go?
I think it is one solution of a few out there, a three phase voltage stabiliser is another and automatic one at that as it appears your voltage balance is somewhat unpredictable.

Now let's be clear here, this is all beyond what we would consider DIY and one should really consider getting a professional out to site and explain what you have to us, even consider having your supply monitored and data logged could give a better idea of the size of the issue if one even exists, we are going on the word of the installer here and it could be he simply made an error in testing, poor contact, cheap measuring instrument or simply fobbing you off to avoid replacing it at his own cost.

I don't think you have a cheap solution unless you want to simply swap the 3ph water pump for a Single phase version but I am not a big fan of going down that road if 3ph is available, single phase pump have more complexity to design so more things can fail, lower available starting torque, shorter life span and less efficient than its 3ph counterpart but it may do the job at the end of the day so like I said, get someone out on site to advice you based on the installation itself and like we are trying to do here - basing it on a mix of electrical theory experience and a few assumptions which may miss something crucial to design and/or advice.

A VSD option is unlikely to be suitable for your pump if it is simply rewound as I suspect it will be sealed and thus selecting the winding arrangements won't be an option unless you request the company to configure it for your VSD 3ph 230v option, this however leaves you with a pump that you simply cannot swap like for like in the future to match the pipework etc as you have customised the pump for yourself, suitable alternatives may exist that are off the shelf though.

If you want to maintain the 3ph pump option it looks like an expensive solution whichever direction you take, you could invest in a single phase pump and even buy a spare for less cost, as you may have found out by now submersible pumps are not cheap to say the least so you going to have to think about what route to take here.
 
Last edited:
Like some of the others I am still sceptical about the original cause of failure. A 2.2kW motor should be protected against catastrophic burnout by its overload protection, regardless of whether the underlying cause is mechanical overload or faulty supply. Before investing in expensive or complex solutions to the voltage imbalance, I would like to see more evidence that it was a key factor in the rapid failure.

Once the pump is returned in working order, I would connect it back up and measure the line currents under working conditions with the typical supply voltages that have been experienced. If the currents are excessive, then one of the solutions discussed will be needed. If not, there is a possibility that the failure was unrelated to the imbalance, however undesirable it might look on paper.
 
Also, remember it is not easy to overheat a submersible pump, the water normally keeps it cool enough even with a small overload
 

Reply to Can a difference in phase voltages cause a motor to fail? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock