Yeah but I'm sure it does all sorts of clever things.... I just don't know how to use them and probably never will!
Don't give upon it...……...after all, you've just learned another way of finding a fault....and that was impossible 24 hrs ago. ;)
 
Yes I could, but would this not just show the 1 or 2 A running through it at that time? It may change rapidly when it's about to trip but I don't think I can get away with standing there for 30 mins :)
Anyway, I am now leaving to find it!
Glad you found it! If you put 10a through a 6a mcb it will take a while to trip, and it wasn't clear if the trip was from overload or fault. The idea was also to work out if it's going down l-n or l-e or l-cpc.
Glad you're sorted though!
 
it wasn't clear if the trip was from overload or fault

I think it was though. HHD reckoned on a couple of amps load on the circuit, and anything else consuming 1500VA or so would have made its presence felt. Had the MCB been tripping through being on the threshold of its current rating, a) it would have been warm which HHD would hopefully have noticed and b) the tripping would be more cyclic than random. It's useful to consider the power dissipated at a suspected fault and what damage it would cause. 1500W dissipated at a point fault would soon set it on fire or melt it so extensively that it could not have remained as it was to cause another trip. So it had to be an intermittent short-circuit, that did not blow itself clear completely on account of the low rating of the MCB and moderately high resistance of the small cable. Had the same damage occurred on a cooker circuit near the board, it would be more likely to blow itself apart at the first bang.

It had classic symptoms of a damaged cable - very low IR L-E and N-E with occasional tripping of the MCB. There was no certainty that each of the abnormal symptoms was related to a single fault but the principle of Occam's razor would suggest so. Easy to analyse with hindsight, of course.
 
Agree totally and thanks for the analysis, i only wanted to add it to the mix as a consideration as no point in saying "i thought that originally" after the fact!
Just a couple of points that may be interesting..
If an MCB trips in overload it can trip again quickly due to it already being very warm
Also the fault i suggested was a faulty psu for lights or similar. A transformer with shorted windings can warm up a lot without causing a fire
 
A great thread complete with a result, thanks Happy for taking the time to give us the result.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Difficult fault to find?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
68

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Genlight,
Replies
68
Views
8,785

Advert