Surely you wouldn't need a 200A sw fuse upstream of the two 100A ones, it would just need to be a switch wouldn't it?
Hypothetical here.... not telling you how to do it.
You have a 140KVA supply
Zs can only be achieved on your side if you fusing to BS88(2) is 125amp or less
You can run 2 x 100amp supplies but issue is they need a common isolation upstream
Fitting a 200amp SW/F upstream would not comply because of Zs failure as 0.15 cannot be acheived.
What will happen in an earth fault then if your Zs is 0.22 instead of 0.15... your cabling could be subject to thermal damage due to the extended duration of the fault, so what are your solutions here?
You can either reduce Zs/Ze which is probably not possible or maybe increase the CSA of the cable proportionally to allow for the extended tripping time... now Ive never needed to do this myself and its hypothetical so would like others input here but if you can get around the issue of the thermal damage to a correctly sized cable then you have taken measures to counteract the poor zs and as its probably for the sake of a few meters of tails that can be housed in steel trunking for added protection then Id be happy with the set-up.
Even I might wear my tin hat for this one lol
The DNO's fusing Zs requirements TBH are their issue if they comply or not but from experience the DNO work to different regs and often in confliction with our own, as is a small supply in the scope of things then full discrimination cannot be achieved and little benefit will be had by derating to 160A customer side.
If the customer has a 200amp (approx' 140KVA) allowance then he should be able to use it all, an O/L will correctly take out the customer fusing first if 200amp BS88's (2) against 200amp BS88 (3) leaving only S/C faults an issue and as I mentioned you can't achieve full discrimination anyway on these small supplies so pointless derating customer upstream fusing.
.