davesparks
So let me get this straight, what you actually want to know is what to do about the fact you have a 200Amp service with a Ze of 0.22 when you need to achieve a Zs on a submain of 0.15?
I have to say it is an interesting question as based on the info supplied it isn't possible.
Off the top of my head I can only come up with splitting the installation into 2 and running a second 125A submain alongside the one you have.
I have to say it is an interesting question as based on the info supplied it isn't possible.
Off the top of my head I can only come up with splitting the installation into 2 and running a second 125A submain alongside the one you have.