Just out of interest, what make/model of earth fault loop tester (presumably MFT) are you using? Some makes are better than others at no-trip Zs measurements through RCDs - on some you get "RCD uplift" of an ohm or so. I suspect the higher the Ze - particularly if it's variable - the more likely you'll get a discrepancy. Using the alternative method of measuring Zs, when there is an RCD present, is often the only way to get a reliable reading.
My concern about your high Ze is that it might be indicitive of a developing fault, one that's getting worse. It might be 1.14Ω this week, but if it's symptomatic of a breakdown in the lead sheath of the supply cable, it might well suddenly go much, much higher. You'll then be relying on main protective bonding for your RCD to work (assuming you've got metal pipes/anything else extraneous).
The DNO are within their rights not to supply a means of earthing if they don't want to. But I'm very surprised at their answer which seems to effectively be, "Yes, we're supplying an earth, but it's not a very good one, so bung an RCD on it."
  • Agree
Reactions: telectrix and DPG
Megger MDT 1553. A’s you say a calculation of the zs would be preferable now, as they have fitted front end RCD so can no longer by pass it for two lead test. Or possibly to fit an eart spike and convert to TT. But as you say I’m surprised that’s how they’ve left it, I’ve not been back to the job yet so I’m only going on what the home owner tells me.
In North West if we is between 0.8 and 1.6 then main fuse de rated and the faulty joint or whatever repaired. Between 1.6 and 20 a temporary RCD would be fitted and again the fault repaired. Over 20 if no RCD on consumer unit supply would be disconnected. The fault repair would be within 7 days, but usually done within one or two days
Thanks for the information I’m in North Wales so I’ll see tomorrow how things have been left with homeowner.
Reactions: DPG
High ze readings. Even higher zs?
Bsharp,
Bsharp,