Hi,

Just a quick question regarding inrush current for my pool lights circuit in my pool/cafe hotel project?

I was looking at 5 of these:
Pool LED - https://www.apollolighting.co.uk/products/pool_led/

125W per light (5x 125 = 625W / 230 = 2.72A)

Issue is that the inrush current per light is 165A (5x 165 = 825A) which will trip the protective device. I know you could use say a type C or D MCB but I cant find a list for Inrush current for MCB's?

Does anyone have link to mcb inrush currents for type b c d etc?



I did see this 16A Inrush current limiter:
Inrush Limiter for LED lighting - https://uk.eaton.com/content/gb/en/products/product-catalog/lighting-controls-inrush-limiter-eaton.html

Any advice would be great?

Thanks

Michael
 
Ok so I assume you are thinking about a B Type 60898?

Why do you think this will trip on an inrush current of 825A?
 
Ok so I assume you are thinking about a B Type 60898?

Why do you think this will trip on an inrush current of 825A?

Ok take a 16A type B as an example:

For this to trip in 0.1 seconds would take 80A & the inrush current per light is 165A (825A for all 5 lights). As the inrush is more it will trip the protective device.

I realise Type B, C & D have the own inrush limits but I cant find these figures so have used the above as an example.

As I understand it inrush current is where the capacitors in this case on the lighting pcb draw current to charge up before the light operates normally. This high current inrush only lasts a split second & then drops back down to normal operating current.


20181117_143713.jpg
 
Last edited:
Ok take a 16A type B as an example:

For this to trip in 0.1 seconds would take 80A & the inrush current per light is 165A (825A for all 5 lights). As the inrush is more it will trip the protective device.

I realise Type B, C & D have the own inrush limits but I cant find these figures so have used the above as an example.

As I understand it inrush current is where the capacitors in this case on the lighting pcb draw current to charge up before the light operates normally. This high current inrush only lasts a split second & then drops back down to normal operating current.


View attachment 45806

You do have a copy of BS7671 and the Type C and Type D tables are directly after the Type B ones.

You also need to find out how long the inrush current lasts for on these fittings.

To me these inrush currents sound quite large. Does the project dictate what fittings you must use?
 
You do have a copy of BS7671 and the Type C and Type D tables are directly after the Type B ones.

Yes was just using type b as an example.
The tables dont show their max inrush currents for each type.

To me these inrush currents sound quite large. Does the project dictate what fitti?

No we can choose the fittings.
 
No graph shows inrush.

If you look at Fig 3A4 & 3A5 you will see a C Type 16A needs 160A to blow in 0.1 and a Type D needs 320A.

So as I see it you have three options. Any idea what those options are?
 
No graph shows inrush.

If you look at Fig 3A4 & 3A5 you will see a C Type 16A needs 160A to blow in 0.1 and a Type D needs 320A.

So as I see it you have three options. Any idea what those options are?

Different lights
Split lights on to multiple circuits
Inrush current limiter

Think I'll go with the inrush current limiter for the project as the lights meet specifications ie ambient temp, anti corrosion, Led efficiency, IP rating etc.
 
  • Agree
Reactions: 1 person
Different lights
Split lights on to multiple circuits
Inrush current limiter

Think I'll go with the inrush current limiter for the project as the lights meet specifications ie ambient temp, anti corrosion, Led efficiency etc.

Bang on. Well done.

I would do the same as you.
 
  • Like
Reactions: Loki
Thanks again
 
  • Like
Reactions: Nigel

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Loki

Arms
~
Joined
Location
Devon
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Inrush current for pool lighting - pool cafe hotel project
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Loki,
Last reply from
Nigel,
Replies
9
Views
149

Advert